Water (Cp = 4.18 kJ/kg.K) at 80°C enters a counter flow heat exchanger with a mass flow rate of 0.5 kg/s. Air (Cp = 1 kJ/kg.K) enters at 30°C with a mass flow rate of 2.09 kg/s. If the effectiveness of the heat exchanger is 0.8, the LMTD (in °C) is
10
This problem involves calculating the Log Mean Temperature Difference (LMTD) for a counter-flow heat exchanger. We are given the fluid properties, mass flow rates, inlet temperatures, and the heat exchanger's effectiveness. Understanding these parameters is crucial for heat exchanger design and analysis, especially when determining the required heat transfer area.
We are provided with the following information for the counter flow heat exchanger:
The heat capacity rate (\(C\)) for each fluid is calculated as the product of its mass flow rate and specific heat capacity. This value represents the rate at which a fluid can absorb or release heat per unit temperature change.
In this problem, we observe that the heat capacity rates for both fluids are equal: \(C_h = C_c = 2.09 \text{ kJ/s.K}\).
The minimum heat capacity rate (\(C_{min}\)) is the smaller of the two calculated heat capacity rates. This is a crucial value as it limits the maximum possible heat transfer in the heat exchanger.
The maximum possible heat transfer (\(Q_{max}\)) occurs if the fluid with the minimum heat capacity rate were to experience the largest possible temperature change, which is the difference between the inlet temperatures of the hot and cold fluids.
The actual heat transfer (\(Q_{actual}\)) that occurs in the heat exchanger is calculated using its given effectiveness and the maximum possible heat transfer.
Using the actual heat transfer rate, we can determine the outlet temperatures of both the hot water and cold air. The heat transferred away from the hot fluid equals the heat absorbed by the cold fluid.
| Fluid | Inlet Temperature (°C) | Outlet Temperature (°C) |
|---|---|---|
| Hot Water | 80 | 40 |
| Cold Air | 30 | 70 |
For a counter-flow heat exchanger, the temperature differences at the two ends (inlet and outlet) are defined as:
Notice that in this specific case, the temperature differences at both ends are equal: \(\Delta T_1 = \Delta T_2 = 10^\circ\text{C}\).
The general formula for LMTD for a counter-flow heat exchanger is:
\[ \text{LMTD} = \frac{\Delta T_1 - \Delta T_2}{\ln\left(\frac{\Delta T_1}{\Delta T_2}\right)} \]However, when the temperature differences at both ends are equal (\(\Delta T_1 = \Delta T_2\)), the LMTD is simply equal to this common temperature difference. This special condition arises when the heat capacity rates of the hot and cold fluids are identical (\(C_h = C_c\)), as seen in this problem.
Since \(\Delta T_1 = \Delta T_2 = 10^\circ\text{C}\), the LMTD is:
\[ \text{LMTD} = 10^\circ\text{C} \]Based on the detailed calculations, the Log Mean Temperature Difference (LMTD) for the given counter-flow heat exchanger operating with water and air is \(10^\circ\text{C}\).
The fin effectiveness can be enhanced by selecting _____ value of heat transfer co-efficient.
NTU, which is a measure of effectiveness of heat exchanger, stands for _________.
LMTD stands for _______.
For a heat exchanger, ΔTmax is the maximum temperature difference and ΔTmin is the minimum temperature difference between the two fluids. LMTD is the log mean temperature difference. Cmin and Cmax are the minimum and the maximum heat capacity rates. The maximum possible heat transfer (Qmax) between the two fluids is
A balanced counter flow heat exchanger has a surface area of 20 m2 and overall heat transfer coefficient of 20 W/m2–K. Air (CP = 1000 J/kg - K) entering at 0.4 kg/s and 280 K is to be preheated by the air leaving the system at 0.4 kg/s and 300 K. The outlet temperature (in K) of the heated air is ___