A balanced counterflow heat exchanger has area 20 m² and overall heat-transfer coefficient 20 W/(m²·K). Each air stream has mass flow 0.4 kg/s and cp = 1000 J/(kg·K). The cold stream enters the exchanger at 280 K and the hot stream enters it at 300 K. The outlet temperature of the heated cold air, in K, is
290
Each heat-capacity rate is 0.4×1000 = 400 W/K, while UA = 400 W/K. Thus NTU = 1 and, for balanced counterflow, ε = NTU/(1+NTU) = 1/2. The cold outlet is 280+0.5(300−280) = 290 K.
The logarithmic mean temperature difference for parallel flow heat exchangers is
The fin effectiveness can be enhanced by selecting _____ value of heat transfer co-efficient.
A cold liquid enters a counter flow heat exchanger at 15 deg at a rate of 8 kg/s. A hot stream of the same liquid enters the heat exchanger at 75 deg at 2 kg/s. Assuming the specific heat of the fluid as 4 kJ/kg.°C, determine the maximum heat transfer rate.
For the same inlet and exit temperatures of the hot and cold fluids, the Log mean temperature difference (LMTD) is
In a heat exchanger, the hot liquid enters with a temperature of 180°C and leaves at 160°C. The cooling fluid enters at 30°C and leaves at 110°C. The capacity ratio of the heat exchanger is