The flow rates of hot and cold water streams running through a parallel flow heat exchanger are 0.2 Kg/sec and 0.5 Kg/sec respectively. The inlet temperatures on hot and cold sides are 75°C and 20°C respectively. The exit temperature of hot water is 45°C. Calculate LMTD of heat exchanger.
29.12°C
This solution details the steps required to calculate the Log Mean Temperature Difference (LMTD) for a heat exchanger operating in a parallel flow configuration. LMTD is essential for determining the heat transfer rate and evaluating the performance of heat exchangers.
The problem provides the following data for the hot and cold water streams:
| Parameter | Hot Water Stream | Cold Water Stream |
|---|---|---|
| Mass Flow Rate ($ \dot{m} $) | 0.2 Kg/sec | 0.5 Kg/sec |
| Inlet Temperature ($ T_{in} $) | 75°C | 20°C |
| Outlet Temperature ($ T_{out} $) | 45°C | To be determined |
To calculate the LMTD, we first need to find the outlet temperature of the cold water stream ($ T_{c,out} $). We can do this by applying the principle of energy balance, assuming the heat lost by the hot fluid equals the heat gained by the cold fluid, and that the specific heat capacities of both fluids are equal.
The energy balance equation is:
$$ \dot{m}_h c_{p,h} (T_{h,in} - T_{h,out}) = \dot{m}_c c_{p,c} (T_{c,out} - T_{c,in}) $$
Assuming \( c_{p,h} = c_{p,c} \), the equation simplifies to:
$$ \dot{m}_h (T_{h,in} - T_{h,out}) = \dot{m}_c (T_{c,out} - T_{c,in}) $$
Substitute the given values:
$$ 0.2 \text{ Kg/sec} \times (75^\circ C - 45^\circ C) = 0.5 \text{ Kg/sec} \times (T_{c,out} - 20^\circ C) $$
Calculate the heat transfer rate on the hot side:
$$ 0.2 \times 30^\circ C = 0.5 \times (T_{c,out} - 20^\circ C) $$
$$ 6 \text{ (Kg \cdot °C)/sec} = 0.5 \text{ Kg/sec} \times (T_{c,out} - 20^\circ C) $$
Now, solve for the cold water outlet temperature ($ T_{c,out} $):
$$ T_{c,out} - 20^\circ C = \frac{6 \text{ (Kg \cdot °C)/sec}}{0.5 \text{ Kg/sec}} $$
$$ T_{c,out} - 20^\circ C = 12^\circ C $$
$$ T_{c,out} = 12^\circ C + 20^\circ C $$
$$ T_{c,out} = 32^\circ C $$
The calculated outlet temperature for the cold water stream is 32°C.
The Log Mean Temperature Difference (LMTD) is calculated using the following formula for a parallel flow heat exchanger:
$$ LMTD = \frac{\Delta T_1 - \Delta T_2}{\ln\left(\frac{\Delta T_1}{\Delta T_2}\right)} $$
Where:
Let's calculate these temperature differences:
Calculate $ \Delta T_1 $:
$$ \Delta T_1 = T_{h,in} - T_{c,in} = 75^\circ C - 20^\circ C = 55^\circ C $$
Calculate $ \Delta T_2 $:
$$ \Delta T_2 = T_{h,out} - T_{c,out} = 45^\circ C - 32^\circ C = 13^\circ C $$
Now, substitute these values into the LMTD formula:
$$ LMTD = \frac{55^\circ C - 13^\circ C}{\ln\left(\frac{55^\circ C}{13^\circ C}\right)} $$
Simplify the numerator:
$$ LMTD = \frac{42^\circ C}{\ln\left(\frac{55}{13}\right)} $$
Calculate the ratio and its natural logarithm:
$$ \frac{55}{13} \approx 4.230769 $$
$$ \ln(4.230769) \approx 1.44225 $$
Finally, calculate the LMTD:
$$ LMTD = \frac{42^\circ C}{1.44225} $$
$$ LMTD \approx 29.12^\circ C $$
The Log Mean Temperature Difference for this parallel flow heat exchanger is approximately 29.12°C.
The fin effectiveness can be enhanced by selecting _____ value of heat transfer co-efficient.
NTU, which is a measure of effectiveness of heat exchanger, stands for _________.
LMTD stands for _______.
Water (Cp = 4.18 kJ/kg.K) at 80°C enters a counter flow heat exchanger with a mass flow rate of 0.5 kg/s. Air (Cp = 1 kJ/kg.K) enters at 30°C with a mass flow rate of 2.09 kg/s. If the effectiveness of the heat exchanger is 0.8, the LMTD (in °C) is
For a heat exchanger, ΔTmax is the maximum temperature difference and ΔTmin is the minimum temperature difference between the two fluids. LMTD is the log mean temperature difference. Cmin and Cmax are the minimum and the maximum heat capacity rates. The maximum possible heat transfer (Qmax) between the two fluids is