The effective length of a compression member whose both ends are fixed in position only is _____.
1L
When designing compression members like columns, it's important to consider how they might buckle under load. The critical buckling load depends not just on the material and cross-section, but also on the length of the member and how its ends are supported. The 'effective length' is a concept used to account for these end support conditions.
The effective length ($L_e$) of a compression member is the length of an equivalent column with pinned ends that would have the same buckling load as the actual column with its specific end conditions. It is calculated using the formula:
$$L_e = K \times L$$
Where:
The value of the effective length factor ($K$) varies significantly based on whether the ends of the compression member are free to rotate, fixed against rotation, fixed in position, or free to move laterally.
Commonly assumed idealised end conditions and their corresponding effective length factors are often represented in tables like the one below:
| End Conditions | Sketch | Theoretical K Value | Recommended Design K Value |
|---|---|---|---|
| Both ends pinned | —O— |
1.0 | 1.0 |
| One end fixed, other end free | —█— |
2.0 | 2.0 |
| One end fixed, other end pinned | —█— |
0.7 | 0.8 |
| Both ends fixed | —█— |
0.5 | 0.65 |
The question asks for the effective length when both ends are fixed in position only. This specific wording means that the ends cannot move horizontally or vertically (their position is fixed), but they are free to rotate. This condition is equivalent to having both ends pinned.
When both ends are pinned (or fixed in position only but free to rotate), the effective length factor $K$ is 1.0.
Using the formula $L_e = K \times L$:
$$L_e = 1.0 \times L = L$$
Therefore, the effective length of a compression member whose both ends are fixed in position only (and free to rotate) is equal to its actual length, $L$.
Looking at the options provided:
The effective length corresponding to both ends fixed in position only (equivalent to pinned-pinned for buckling) is 1L.
What will be the effective length of a column of length L (compression member) fixed at one end and hinged at other end i.e. restrained in position but not in rotation?
What will be the effective length of a column of length L (compression member) fixed at both ends i.e. restrained in position and rotation?
What is the recommended value of effective length for a column held in position and restrained against rotation at one end, and at the other end restrained against rotation but not held in position?
A steel column (f y= 250 N/mm 2, and f cd = 200 N/mm 2) of effective sectional area 6000 mm 2 will have strength equal to _____.