Select the relay type that compares currents at two points to detect faults within a protected zone.

This question was previously asked in
RRB NTPC 2025 Graduate Level CBT 1 Question Paper (25-Mar-2026) (Shift 3)
The correct answer is

Differential relay

The question asks for the type of relay that compares currents at two points to detect faults within a protected zone. To answer this, we need to understand the function of each relay type mentioned in the options:

  1. Inverse Time Overcurrent Relay: This type of relay operates when the current exceeds a predetermined value and the operation time is inversely proportional to the magnitude of the current. It does not typically compare currents at two different points.
  2. Distance Relay: This relay measures the impedance between the protection relay and the fault location. It is used mainly for line protection and does not directly compare currents at two different points.
  3. Differential Relay: The primary function of a differential relay is to compare the current entering and leaving a protected section. It operates if there is a difference between these currents, indicating a fault within the protection zone.
  4. Instantaneous Overcurrent Relay: This relay operates immediately when the current exceeds its setting, without intentional delay. It also does not compare currents at two different points.

From the above explanation, we can see that the differential relay is specifically designed to compare currents at two points to detect electrical faults within a protected zone. This type of relay is used in systems where precise fault detection is crucial, as it ensures that only internal faults within the defined zone cause a trip.

Conclusion: The correct answer is Differential Relay.

Was this answer helpful?

Similar Questions

  1. A control circuit uses a timer relay to switch ON a load after a set delay. If the load energizes immediately when the circuit is powered, what is most likely wrong?

  2. In a control panel, why is it necessary to select a contactor with a higher making capacity than the running current of the connected load?


Important Questions from Relays and Voltage Regulators

  1. A control circuit uses a timer relay to switch ON a load after a set delay. If the load energizes immediately when the circuit is powered, what is most likely wrong?

  2. In a control panel, why is it necessary to select a contactor with a higher making capacity than the running current of the connected load?

Need Expert Advice?
Upcoming Exams
RRB NTPC
September 27, 2026
Test Series
RRB ALP img
Railways
RRB ALP 2026 Mock Test series
1035 Tests 1 Tests Free
749 Attempts
4.3(233)
English, Hindi
More Questions from RRB ALP

Start Your Preparation with Prepp Mobile App

Download the app from Google Play & App Store
Download the app from Google Play & App Store
Prepp Mobile App