Loads applied on a slab, such as floor or roof loads, are transferred to supporting structural elements. When a slab is supported by beams, the load transfer primarily occurs at the interface between the slab and the beam.
The primary way a slab transfers its load to a supporting beam is through the development of forces at their connection point.
Therefore, the shearing force is the most direct and primary way the load moves from the slab to the beam.
A simply supported RCC beam of span 4 m is supporting a brick wall over its entire span. The brick wall is 250 mm thick and 2 m high. The RCC beam has a depth of 600 mm and width of 250 mm. The density of brick masonry and RCC can be assumed as 18 KN/m³ and 25 KN/m³ respectively. Considering the load of the wall and self-weight of the RCC beam, the maximum bending moment in the beam (in KN-m) will be ____________ [rounded off to two decimal places].

A simply supported beam having effective span of 5 meter is carrying a centrally concentrated load of 16 kN. The maximum bending moment in the beam in kN-m is _______________
Area of tensile steel per meter width of a reinforced concrete slab is 335 sq mm. If 8 mm rods are used as reinforcement, then centre to centre spacing of the reinforcement in mm is _______________