In symmetrical fault calculations, percentage reactance at base kVA is equal to
base kVA/rated kVA × % reactance at rated kVA
In the study of power systems, especially during symmetrical fault calculations, it is crucial to standardize electrical quantities. The per unit (p.u.) system or percentage system is widely used for this purpose as it simplifies complex calculations by expressing all values relative to a common base. When different components of a power system have their ratings given (e.g., rated kVA), it becomes necessary to convert their parameters, such as percentage reactance, to a single chosen system-wide base kVA.
The concept of a base kVA is fundamental in the per unit system. It is a reference apparent power value chosen for the entire system or a specific zone within it. All power quantities are then expressed as a fraction or percentage of this base value. Similarly, the percentage reactance (%X) of a component indicates its reactance relative to its rated capacity or a specified base.
The per unit value of any quantity is defined as:
For reactance, the per unit value at a specific base kVA and base voltage is given by:
When you change the base kVA, the per unit or percentage reactance value also changes proportionally, assuming the base voltage remains constant. This transformation is vital to ensure all reactances are on a common reference before performing symmetrical fault calculations.
To convert the percentage reactance of a component from an initial base (often its rated kVA) to a new base kVA, a specific formula is used. This formula ensures that the relative opposition to current flow is accurately represented under the new base conditions.
The relationship between the per unit reactance at two different base kVAs (assuming constant base voltage) is:
Since percentage reactance is simply the per unit reactance multiplied by 100, we can write the formula for percentage reactance conversion as:
In the context of the question, the 'old base' is the rated kVA of the equipment, and the 'new base' is the desired common base kVA for the system's symmetrical fault calculations.
Therefore, the percentage reactance at base kVA is equal to:
Let's evaluate the given options based on the derived formula for converting percentage reactance to a common base kVA in symmetrical fault calculations.
| Option | Expression | Explanation |
|---|---|---|
| 1 | $\text{base kVA / rated kVA} \times \text{\% reactance at rated kVA}$ | This expression correctly represents the formula for converting percentage reactance from its rated kVA to a new base kVA. It multiplies the original percentage reactance by the ratio of the new base kVA to the original rated kVA. This is the standard method used in power system analysis. |
| 2 | $\text{base kVA / rated kVA} \times \text{\% capacitance at rated kVA}$ | This option is incorrect because it uses 'percentage capacitance' instead of 'percentage reactance'. The formula specifically applies to reactance (or impedance), not capacitance directly in this context for base conversion. |
| 3 | $\text{base kVA} \times \text{rated kVA} \times \text{\% reactance at rated kVA}$ | This option is incorrect as it multiplies the base kVA and rated kVA instead of taking their ratio. This would lead to a significantly different and incorrect value for the percentage reactance at the new base. |
| 4 | none of the above | This option is incorrect as option 1 accurately provides the formula. |
Based on the principles of base conversion in power system analysis, the correct way to find the percentage reactance at base kVA from its value at rated kVA is to use the direct proportionality with the kVA base change.
The relation between the old and new per unit impedance values is given by:
A synchronous generator is rated at 40 MVA, 14.6 kV and 50 Hz. The base impedance of the generator will be
The per unit impedance of a line is X p.u. If base voltage is tripled and base MVA is doubled, the new per unit impedance is: