A synchronous generator is rated at 40 MVA, 10 kV and 50 Hz. The base impedance of the generator will be:
2.5 Ω
Understanding the base impedance is crucial in power system analysis, especially when working with per-unit systems. The base impedance provides a reference value against which all other impedances in the system are normalized. For a three-phase system like a synchronous generator, the base impedance can be calculated using the generator's base apparent power (MVA) and base voltage (kV).
The base impedance ($\text{Z}_{\text{base}}$) for a three-phase system is derived from the base voltage ($\text{V}_{\text{base}}$) and base apparent power ($\text{S}_{\text{base}}$) using the following formula:
$$\text{Z}_{\text{base}} = \frac{(\text{V}_{\text{base}})^2}{\text{S}_{\text{base}}}$$
Where:
From the question, we are provided with the following specifications for the synchronous generator:
To find the base impedance of the synchronous generator, we substitute the given values into the formula:
$$\text{Z}_{\text{base}} = \frac{(\text{V}_{\text{base}})^2}{\text{S}_{\text{base}}}$$
Substitute $\text{V}_{\text{base}} = 10 \text{ kV}$ and $\text{S}_{\text{base}} = 40 \text{ MVA}$:
$$\text{Z}_{\text{base}} = \frac{(10 \text{ kV})^2}{40 \text{ MVA}}$$
First, calculate the square of the base voltage:
$$(10 \text{ kV})^2 = 100 \text{ (kV)}^2$$
Now, perform the division:
$$\text{Z}_{\text{base}} = \frac{100 \text{ (kV)}^2}{40 \text{ MVA}}$$
$$\text{Z}_{\text{base}} = 2.5 \text{ } \Omega$$
Therefore, the base impedance of the synchronous generator is 2.5 Ohms.
Let's compare our calculated base impedance with the given options:
| Option | Value |
|---|---|
| 1 | 10 $\Omega$ |
| 2 | 5 $\Omega$ |
| 3 | 7.5 $\Omega$ |
| 4 | 2.5 $\Omega$ |
The calculated base impedance of 2.5 $\Omega$ matches Option 4.
The relation between the old and new per unit impedance values is given by:
A synchronous generator is rated at 40 MVA, 14.6 kV and 50 Hz. The base impedance of the generator will be
The per unit impedance of a line is X p.u. If base voltage is tripled and base MVA is doubled, the new per unit impedance is:
In symmetrical fault calculations, percentage reactance at base kVA is equal to