A synchronous generator is rated at 40 MVA, 14.6 kV and 50 Hz. The base impedance of the generator will be

The correct answer is

5.33 Ω

Synchronous Generator Base Impedance Calculation

Understanding the base impedance is crucial in power system analysis, especially when dealing with per-unit systems. For a synchronous generator, the base impedance provides a reference value against which all other impedances in the system can be normalized. This question asks us to calculate the base impedance of a synchronous generator given its apparent power rating (MVA) and voltage rating (kV).

Generator Parameters

First, let's list the given parameters of the synchronous generator:

  • Apparent Power Rating (\(S_{base}\)): 40 MVA
  • Line Voltage Rating (\(V_{base}\)): 14.6 kV
  • Frequency (\(f\)): 50 Hz

The frequency is provided but is not directly used in the calculation of the base impedance, which primarily depends on the voltage and apparent power ratings.

Base Impedance Formula

The base impedance (\(Z_{base}\)) for a three-phase system like a synchronous generator can be calculated using the following formula:

\[ Z_{base} = \frac{(V_{base})^2}{S_{base}} \]

Where:

  • \(Z_{base}\) is the base impedance in Ohms (\(\Omega\)).
  • \(V_{base}\) is the line-to-line base voltage in kilovolts (kV).
  • \(S_{base}\) is the three-phase base apparent power in megavolt-amperes (MVA).

Calculating Generator Base Impedance

Now, let's substitute the given values into the formula:

\[ V_{base} = 14.6 \text{ kV} \]

\[ S_{base} = 40 \text{ MVA} \]

Applying the formula:

\[ Z_{base} = \frac{(14.6 \text{ kV})^2}{40 \text{ MVA}} \]

\[ Z_{base} = \frac{14.6 \times 14.6}{40} \Omega \]

\[ Z_{base} = \frac{213.16}{40} \Omega \]

\[ Z_{base} = 5.329 \Omega \]

Rounding the value to two decimal places, we get:

\[ Z_{base} \approx 5.33 \Omega \]

Final Impedance Conclusion

The calculated base impedance for the synchronous generator is approximately 5.33 \(\Omega\). This value is crucial for converting actual impedances to a per-unit system, simplifying power system calculations and comparisons.

Was this answer helpful?

Important Questions from Per Unit System

  1. The relation between the old and new per unit impedance values is given by:

  2. The per unit impedance Z (Pu) in 3 - phase system is -
  3. A synchronous generator is rated at 40 MVA, 10 kV and 50 Hz. The base impedance of the generator will be:
  4. The per unit impedance of a line is X p.u. If base voltage is tripled and base MVA is doubled, the new per unit impedance is:

  5. In symmetrical fault calculations, percentage reactance at base kVA is equal to

Need Expert Advice?

Start Your Preparation with Prepp Mobile App

Download the app from Google Play & App Store
Download the app from Google Play & App Store
Prepp Mobile App