In a three-phase system with a line-to-line voltage of 400 V and a line current of 10 A, what is the total real power in Watt, delivered to the load if the power factor is 0.9?
3600√3 W
The total real power in a three-phase system can be calculated using the following formula:
\(P = \sqrt{3} V_{L} I_{L} \cos(\phi)\)
Where:
Substituting the given values into the formula:
\(P = \sqrt{3} \times 400 V \times 10 A \times 0.9\)
\(P = 3600\sqrt{3} W\)
Therefore, the total real power delivered to the load is \(3600\sqrt{3} W\).