In a parallel flow heat exchanger operating under steady state, the heat capacity rates (product of specific heat at constant pressure and mass flow rate) of the hot and cold fluid are equal. The hot fluid, flowing at 1 kg/s with Cp = 4 kJ/kgK, enters the heat exchanger at 102°C while the cold fluid has an inlet temperature of 15°C. The overall heat transfer coefficient for the heat exchanger is estimated to be 1 kW/m2K and the corresponding heat transfer surface area is 5 m2. Neglect heat transfer between the heat exchanger and the ambient. The heat exchanger is characterized by the following relation:

2ϵ = 1 – exp (−2NTU) .

The exit temperature (in °C) for the cold fluid is

The correct answer is

55

Cmin=1×4=4 kW/K and NTU=UA/Cmin=5/4=1.25. Effectiveness is (1−e^(−2.5))/2=0.45896. The cold outlet is 15+0.45896(102−15)=54.93°C≈55°C.

Was this answer helpful?

Important Questions from Heat Exchanger Analysis

  1. The logarithmic mean temperature difference for parallel flow heat exchangers is

  2. The fin effectiveness can be enhanced by selecting _____ value of heat transfer co-efficient.

  3. A cold liquid enters a counter flow heat exchanger at 15 deg at a rate of 8 kg/s. A hot stream of the same liquid enters the heat exchanger at 75 deg at 2 kg/s. Assuming the specific heat of the fluid as 4 kJ/kg.°C, determine the maximum heat transfer rate.

  4. For the same inlet and exit temperatures of the hot and cold fluids, the Log mean temperature difference (LMTD) is

  5. In a heat exchanger, the hot liquid enters with a temperature of 180°C and leaves at 160°C. The cooling fluid enters at 30°C and leaves at 110°C. The capacity ratio of the heat exchanger is

Need Expert Advice?

Start Your Preparation with Prepp Mobile App

Download the app from Google Play & App Store
Download the app from Google Play & App Store
Prepp Mobile App