For the same inlet and exit temperatures of the hot and cold fluids, the Log mean temperature difference (LMTD) is
Greater for counter flow heat exchanger than the parallel flow heat exchanger.
The Log Mean Temperature Difference (LMTD) is a crucial parameter in heat exchanger design and analysis. It represents the logarithmic average of the temperature difference between the hot and cold fluid streams at the two ends of the heat exchanger. The fundamental equation for heat transfer in a heat exchanger is given by:
$ Q = U \times A \times LMTD $
where Q is the rate of heat transfer, U is the overall heat transfer coefficient, and A is the heat transfer surface area.
Heat exchangers can be designed with different flow arrangements for the hot and cold fluids. The two most common are parallel flow and counter flow.
The formula for LMTD is the same regardless of the flow arrangement:
$ LMTD = \frac{\Delta T_1 - \Delta T_2}{\ln(\Delta T_1 / \Delta T_2)} $
However, the values of the temperature differences at the two ends, $\Delta T_1$ and $\Delta T_2$, depend on the flow configuration:
When the inlet and exit temperatures of the fluids are the same for both arrangements (i.e., $ T_{h,in}, T_{h,out}, T_{c,in}, T_{c,out} $ are fixed), the terminal temperature differences in the counter flow setup ($ T_{h,in} - T_{c,out} $ and $ T_{h,out} - T_{c,in} $) are generally larger than those in the parallel flow setup ($ T_{h,in} - T_{c,in} $ and $ T_{h,out} - T_{c,out} $).
Consider a case where $ T_{h,in} > T_{c,in} $ and $ T_{h,out} > T_{c,out} $. For the same temperatures, the counter flow differences ($ T_{h,in} - T_{c,out} $ and $ T_{h,out} - T_{c,in} $) result in a larger LMTD compared to the parallel flow differences ($ T_{h,in} - T_{c,in} $ and $ T_{h,out} - T_{c,out} $). A larger LMTD implies a more efficient heat transfer for a given heat exchanger size (area A) and overall coefficient (U).
Therefore, for the same inlet and exit temperatures of the hot and cold fluids, the Log Mean Temperature Difference (LMTD) is greater for a counter flow heat exchanger than for a parallel flow heat exchanger.
The fin effectiveness can be enhanced by selecting _____ value of heat transfer co-efficient.
NTU, which is a measure of effectiveness of heat exchanger, stands for _________.
LMTD stands for _______.
Water (Cp = 4.18 kJ/kg.K) at 80°C enters a counter flow heat exchanger with a mass flow rate of 0.5 kg/s. Air (Cp = 1 kJ/kg.K) enters at 30°C with a mass flow rate of 2.09 kg/s. If the effectiveness of the heat exchanger is 0.8, the LMTD (in °C) is
For a heat exchanger, ΔTmax is the maximum temperature difference and ΔTmin is the minimum temperature difference between the two fluids. LMTD is the log mean temperature difference. Cmin and Cmax are the minimum and the maximum heat capacity rates. The maximum possible heat transfer (Qmax) between the two fluids is