Consider three transformers in Δ - Δ, supplying their rated load. If one transformer is removed, then each of the remaining two transformers is overloaded. The overload on each transformer is given as
1.732
This question examines the overload condition of transformers when a Delta-Delta ($\Delta$-$\Delta$) three-phase bank operating at rated load experiences the removal of one transformer, leading to an open-delta configuration.
In a standard Delta-Delta connection supplying a balanced three-phase load, each of the three single-phase transformers carries a specific portion of the total load. Let's define the key parameters:
$$S_{rated} = V_{ph} \times I_{ph} = V_L \times \frac{I_L}{\sqrt{3}}$$
$$S_{total} = 3 \times S_{rated} = 3 \times \left( V_L \times \frac{I_L}{\sqrt{3}} \right) = \sqrt{3} V_L I_L$$
When one transformer is removed from the $\Delta$-$\Delta$ bank, the remaining two transformers must supply the original total load ($S_{total}$) but now operate in an open-delta configuration.
$$S_{actual} = V_L \times I_{actual\_ph} = V_L \times I_L$$
The overload factor quantifies how much the actual power handled by a transformer exceeds its rated power. It is calculated as the ratio of the actual apparent power ($S_{actual}$) to the rated apparent power ($S_{rated}$):
$$ \text{Overload Factor} = \frac{S_{actual}}{S_{rated}} $$
By substituting the derived expressions for $S_{actual}$ and $S_{rated}$ into the formula:
$$ \text{Overload Factor} = \frac{V_L \times I_L}{V_L \times \frac{I_L}{\sqrt{3}}} $$
Simplifying this mathematical expression gives:
$$ \text{Overload Factor} = \frac{I_L}{\frac{I_L}{\sqrt{3}}} = \sqrt{3} $$
The calculated overload factor is $\sqrt{3}$. The numerical value of $\sqrt{3}$ is approximately $1.732$. This result indicates that each of the two transformers operating in the open-delta configuration is forced to handle approximately $1.732$ times its rated apparent power (kVA) to meet the demands of the original full load.
Three-phase transformer contains-
Which type of connection is used for both large voltage and low voltage rating transformers?
In Three Phase Transformer, The load Current is 139.1 A, and Secondary Voltage is 415 V. The Rating of the Transformer would be:
The core of a three-phase, 50 Hz, 1000/400 V delta/star: 300 kVA core type transformer operated with a flux of 0.04 wb. Find the EMF per turn.
A three-phase transformer has 600 primary turns and 200 secondary turns. If the supply voltage is 1000 V, find the secondary line voltage on no-load when the windings are connected in star–delta.