Consider three transformers in Δ - Δ, supplying their rated load. If one transformer is removed, then each of the remaining two transformers is overloaded. The overload on each transformer is given as

The correct answer is

1.732

Transformer Overload Analysis in Open Delta Operation

This question examines the overload condition of transformers when a Delta-Delta ($\Delta$-$\Delta$) three-phase bank operating at rated load experiences the removal of one transformer, leading to an open-delta configuration.

Understanding the Initial $\Delta$-$\Delta$ Setup

In a standard Delta-Delta connection supplying a balanced three-phase load, each of the three single-phase transformers carries a specific portion of the total load. Let's define the key parameters:

  • Let $S_{rated}$ represent the rated apparent power (in kVA) of each individual transformer in the bank.
  • The system operates with a line voltage $V_L$ and draws a line current $I_L$.
  • In a $\Delta$ connection, the voltage across each transformer winding (phase voltage) is equal to the line voltage: $V_{ph} = V_L$.
  • The current flowing through each transformer winding (phase current) relates to the line current by: $I_{ph} = \frac{I_L}{\sqrt{3}}$.
  • Using these values, the rated kVA of each transformer can be expressed as:

    $$S_{rated} = V_{ph} \times I_{ph} = V_L \times \frac{I_L}{\sqrt{3}}$$

  • The total apparent power supplied by the complete three-transformer bank is the sum of the power handled by each unit:

    $$S_{total} = 3 \times S_{rated} = 3 \times \left( V_L \times \frac{I_L}{\sqrt{3}} \right) = \sqrt{3} V_L I_L$$

Operation in Open-Delta Configuration

When one transformer is removed from the $\Delta$-$\Delta$ bank, the remaining two transformers must supply the original total load ($S_{total}$) but now operate in an open-delta configuration.

  • The connected load continues to demand the same line voltage $V_L$ and line current $I_L$.
  • In the open-delta connection, the two remaining transformers are connected across two lines of the three-phase system.
  • The voltage across the windings of each of these two transformers remains the line voltage, $V_L$.
  • However, the current that flows through the windings of each of the two operating transformers increases to become equal to the line current: $I_{actual\_ph} = I_L$.
  • Consequently, the actual apparent power handled by each transformer in this open-delta setup is calculated as:

    $$S_{actual} = V_L \times I_{actual\_ph} = V_L \times I_L$$

Determining the Overload Factor

The overload factor quantifies how much the actual power handled by a transformer exceeds its rated power. It is calculated as the ratio of the actual apparent power ($S_{actual}$) to the rated apparent power ($S_{rated}$):

$$ \text{Overload Factor} = \frac{S_{actual}}{S_{rated}} $$

By substituting the derived expressions for $S_{actual}$ and $S_{rated}$ into the formula:

$$ \text{Overload Factor} = \frac{V_L \times I_L}{V_L \times \frac{I_L}{\sqrt{3}}} $$

Simplifying this mathematical expression gives:

$$ \text{Overload Factor} = \frac{I_L}{\frac{I_L}{\sqrt{3}}} = \sqrt{3} $$

Quantifying the Overload Magnitude

The calculated overload factor is $\sqrt{3}$. The numerical value of $\sqrt{3}$ is approximately $1.732$. This result indicates that each of the two transformers operating in the open-delta configuration is forced to handle approximately $1.732$ times its rated apparent power (kVA) to meet the demands of the original full load.

Was this answer helpful?

Important Questions from Three Phase Transformer Basics

  1. Three-phase transformer contains-

  2. Which type of connection is used for both large voltage and low voltage rating transformers?

  3. In Three Phase Transformer, The load Current is 139.1 A, and Secondary Voltage is 415 V. The Rating of the Transformer would be:

  4. The core of a three-phase, 50 Hz, 1000/400 V delta/star: 300 kVA core type transformer operated with a flux of 0.04 wb. Find the EMF per turn.

  5. A three-phase transformer has 600 primary turns and 200 secondary turns. If the supply voltage is 1000 V, find the secondary line voltage on no-load when the windings are connected in star–delta.