A three-phase 33 kV, oil-circuit breaker is rated 1500 A, 2000 MVA, 2 s. The symmetrical breaking current for this breaker would be

The correct answer is 35 kA

Understanding Symmetrical Breaking Current

The symmetrical breaking current is a crucial parameter for an oil-circuit breaker. It represents the RMS value of the AC component of the current that the circuit breaker is expected to interrupt during a symmetrical short circuit. This value is typically derived from the circuit breaker's MVA rating and the system voltage.

Circuit Breaker Ratings Analysis

The provided details for the three-phase oil-circuit breaker are:

  • System Voltage: 33 kV (Line Voltage)
  • Rated Current: 1500 A
  • MVA Rating: 2000 MVA
  • Rated Time: 2 s

The symmetrical breaking current calculation primarily relies on the MVA rating and the system's line voltage.

Calculating Symmetrical Breaking Current

The formula to calculate the symmetrical breaking current ($I_{sc}$) in Amperes (A) is:

$$ I_{sc} = \frac{MVA \times 1000}{\sqrt{3} \times V_{L}} $$

Where:

  • MVA is the apparent power rating in Megavolt-Amperes.
  • $V_{L}$ is the system line voltage in kilovolts (kV).
  • The factor 1000 is used to convert MVA to kVA.
  • The factor $\sqrt{3}$ is used because the system is three-phase.

Step-by-Step Calculation

  1. Substitute the given values into the formula:

    MVA = 2000

    $V_{L}$ = 33 kV

    $$ I_{sc} = \frac{2000 \times 1000}{\sqrt{3} \times 33} $$

  2. Calculate the denominator:

    $\sqrt{3} \times 33 \approx 1.732 \times 33$

    $\sqrt{3} \times 33 \approx 57.156$

  3. Calculate the current:

    $$ I_{sc} = \frac{2,000,000}{57.156} $$

    $$ I_{sc} \approx 35000 \text{ A} $$

  4. Convert the current to kiloamperes (kA):

    $$ I_{sc} \approx \frac{35000}{1000} \text{ kA} $$

    $$ I_{sc} \approx 35 \text{ kA} $$

Conclusion

Based on the calculation using the MVA rating and system voltage, the symmetrical breaking current for the three-phase oil-circuit breaker is approximately 35 kA. This value is essential for ensuring the circuit breaker can safely interrupt fault currents within its specified limits.

Was this answer helpful?

Important Questions from Ratings of Circuit Breakers

  1. The highest rating of Triple pole with Neutral (TPN) MCB main switches available in the local market is _______.

  2. Which of the following fuses has the highest rating?

  3. A three - phase, 33 kV oil circuit breaker is rated 1200 A, 2000 MVA, 3s. The symmetrical breaking current is -

  4. A three-phase, 33 kV oil circuit breaker is rated 1200 A, 2000 MVA, 3 s. The symmetrical breaking current is

  5. In circuit breakers, which of the following methods is a NOT a correct method of increasing arc resistance?
Need Expert Advice?

Start Your Preparation with Prepp Mobile App

Download the app from Google Play & App Store
Download the app from Google Play & App Store
Prepp Mobile App