A three-phase 33 kV, oil-circuit breaker is rated 1500 A, 2000 MVA, 2 s. The symmetrical breaking current for this breaker would be
The symmetrical breaking current is a crucial parameter for an oil-circuit breaker. It represents the RMS value of the AC component of the current that the circuit breaker is expected to interrupt during a symmetrical short circuit. This value is typically derived from the circuit breaker's MVA rating and the system voltage.
The provided details for the three-phase oil-circuit breaker are:
The symmetrical breaking current calculation primarily relies on the MVA rating and the system's line voltage.
The formula to calculate the symmetrical breaking current ($I_{sc}$) in Amperes (A) is:
$$ I_{sc} = \frac{MVA \times 1000}{\sqrt{3} \times V_{L}} $$
Where:
MVA = 2000
$V_{L}$ = 33 kV
$$ I_{sc} = \frac{2000 \times 1000}{\sqrt{3} \times 33} $$
$\sqrt{3} \times 33 \approx 1.732 \times 33$
$\sqrt{3} \times 33 \approx 57.156$
$$ I_{sc} = \frac{2,000,000}{57.156} $$
$$ I_{sc} \approx 35000 \text{ A} $$
$$ I_{sc} \approx \frac{35000}{1000} \text{ kA} $$
$$ I_{sc} \approx 35 \text{ kA} $$
Based on the calculation using the MVA rating and system voltage, the symmetrical breaking current for the three-phase oil-circuit breaker is approximately 35 kA. This value is essential for ensuring the circuit breaker can safely interrupt fault currents within its specified limits.