All Exams Test series for 1 year @ ₹349 only
Question

What is the condition at which a transformer gives maximum efficiency?

The correct answer is

When iron loss equals copper loss

Transformer Maximum Efficiency Condition Explained

A transformer is a static electrical machine used to transfer power from one circuit to another without changing the frequency. The efficiency of a transformer is defined as the ratio of output power to input power. In an ideal transformer, efficiency would be 100%, but in real transformers, there are losses.

The input power to a transformer is equal to the output power plus the losses. Therefore, efficiency ($\eta$) can be expressed as:

$\eta = \frac{\text{Output Power}}{\text{Input Power}} = \frac{\text{Output Power}}{\text{Output Power} + \text{Losses}}$

The losses in a transformer consist of two main types:

  • Iron Losses (Core Losses): These losses occur in the core of the transformer due to hysteresis and eddy currents. Iron losses ($P_i$) depend on the voltage and frequency and are practically constant regardless of the load.
  • Copper Losses ($I^2R$ Losses): These losses occur in the windings due to the resistance of the copper wire. Copper losses ($P_{cu}$) are proportional to the square of the load current ($I_2^2$) and the winding resistance ($R_{eq}$ referred to the secondary). So, $P_{cu} = I_2^2 R_{eq}$. These losses vary with the load.

Let the secondary terminal voltage be $V_2$ and the load current be $I_2$. If the power factor of the load is $\cos\phi_2$, the output power is $V_2 I_2 \cos\phi_2$.

The total losses are $P_{\text{losses}} = P_i + P_{cu}$.

So, the efficiency can be written as:

$\eta = \frac{V_2 I_2 \cos\phi_2}{V_2 I_2 \cos\phi_2 + P_i + I_2^2 R_{eq}}$

To find the condition for maximum efficiency, we can differentiate the efficiency expression with respect to the variable load (represented by the load current $I_2$) and set the derivative to zero. Assuming $V_2$, $\cos\phi_2$, $P_i$, and $R_{eq}$ are constant for a specific operating condition (like full load voltage and a particular power factor), the efficiency varies only with $I_2$.

Maximum efficiency occurs when the variable losses (Copper Losses) equal the constant losses (Iron Losses).

Mathematically, maximum efficiency is achieved when:

$\frac{d\eta}{dI_2} = 0$

This differentiation yields the condition:

$I_2^2 R_{eq} = P_i$

Which means:

Copper Loss = Iron Loss

At maximum efficiency, the load current $I_{2(\text{max eff})}$ is such that $I_{2(\text{max eff})}^2 R_{eq} = P_i$.

Therefore, the transformer gives maximum efficiency when its copper losses are equal to its iron losses. This condition balances the constant core losses with the load-dependent copper losses to achieve the highest ratio of output to input power.

Let's look at the given options:

  • When iron loss is greater than copper loss - This is not the condition for maximum efficiency.
  • When iron loss is zero - Iron loss is a constant loss in a real transformer; it is not zero.
  • When iron loss equals copper loss - As derived, this is the condition for maximum efficiency.
  • When iron loss is half of the copper loss - This is not the condition for maximum efficiency.

Based on the analysis, the condition for a transformer to give maximum efficiency is when the iron loss is equal to the copper loss.

Was this answer helpful?

Important Questions from Transformer Copper Losses

  1. For a single phase transformer, the maximum efficiency occurs at 75% of the load, then \(\rm \frac{iron \ loss \ at\ full \ load }{copper \ loss \ at\ full \ load}=?\)

  2. In a single-phase transformer, the ratio of transformation is 2 and the secondary resistance is 0.24 Ω. Find the resistance of secondary in terms of primary.

  3. The full load copper loss and iron loss of a transformer are 6400 W and 5000 W respectively the copper loss and iron loss at half load will be respectively.

  4. Which of the following losses remains variable during normal operation of transformer?
  5. A single-phase \(400\;V,\;50\;Hz\) transformer has an iron loss of \(5000\;W\) at the rated condition. When operated at \(200\;V,\;25\;Hz\), the iron loss is \(2000\;W\). When operated at \(416\;V,\;52\;Hz\), the value of the hysteresis loss divided by the eddy current loss is ______.

Need Expert Advice?

Start Your Preparation with Prepp Mobile App

Download the app from Google Play & App Store
Download the app from Google Play & App Store
Prepp Mobile App