Two generators have cost functions F1 and F2. Their incremental-cost characteristics are \(\frac{{d{F_1}}}{{d{P_1}}} = 40 + 0.2{P_1}\) \(\frac{{d{F_2}}}{{d{P_2}}} = 32 + 0.4{P_2}\) They need to deliver a combined load of 260 MW. Ignoring network losses, for economic operation, the generations P1 and P2 (in MW) are
P1 = 160, P2 = 100
This problem asks us to find the optimal generation amounts, $P_1$ and $P_2$, for two generators to meet a total load of 260 MW while minimizing the total cost. The key principle for economic operation, ignoring network losses, is that the incremental cost (the cost to produce one additional MW) must be the same for both generators.
We are given the incremental cost functions for the two generators:
Here, $\frac{{d{F}}}{{d{P}}}$ represents the marginal cost of generating power $P$ for a specific generator.
For the most economical operation, the marginal costs of both generators must be equal:
$$ \frac{{d{F_1}}}{{d{P_1}}} = \frac{{d{F_2}}}{{d{P_2}}} $$
We set the two incremental cost functions equal to each other:
$$ 40 + 0.2{P_1} = 32 + 0.4{P_2} $$
Rearranging this equation:
$$ 0.2{P_1} - 0.4{P_2} = 32 - 40 $$
$$ 0.2{P_1} - 0.4{P_2} = -8 $$
To simplify, we can multiply the entire equation by 10:
$$ 2{P_1} - 4{P_2} = -80 $$
Dividing by 2:
$$ P_1 - 2{P_2} = -40 \quad (*) $$
We also know the total load requirement:
$$ P_1 + P_2 = 260 \, \text{MW} $$
From this total load equation, we can express $P_1$ in terms of $P_2$:
$$ P_1 = 260 - P_2 $$
Now, substitute this expression for $P_1$ into the simplified incremental cost equation ($*$):
$$ (260 - P_2) - 2{P_2} = -40 $$
Combine the $P_2$ terms:
$$ 260 - 3{P_2} = -40 $$
Solve for $P_2$:
$$ 3{P_2} = 260 + 40 $$
$$ 3{P_2} = 300 $$
$$ P_2 = \frac{300}{3} $$
$$ P_2 = 100 \, \text{MW} $$
Finally, substitute the value of $P_2$ back into the equation for $P_1$:
$$ P_1 = 260 - P_2 $$
$$ P_1 = 260 - 100 $$
$$ P_1 = 160 \, \text{MW} $$
Let's check if these values satisfy the conditions:
Therefore, the economic generation schedule is $P_1 = 160$ MW and $P_2 = 100$ MW.
The generation amounts that ensure economic operation for the combined load of 260 MW are $P_1 = 160$ MW and $P_2 = 100$ MW.
Which of the following devices is suitable for the removal of gaseous pollutants?
The connected load of a consumer is 3 kW and his maximum demand is 1.5 kW. The demand factor of the consumer is
The maximum demand of a consumer is 2 kW and his daily energy consumption is 24 units. His load factor is ______.
The decrease in the value of the power plant / electrical equipment and building due to constant use is known as:
Which component of the total cost of electrical energy is proportional to the energy generated (kWh)?