Question

The total core loss of a specimen of silicon steel is found to be 1500 W at 50 Hz. Keeping the flux density constant, the loss becomes 3000 W when the frequency is raised to 75 Hz. The eddy current loss at 75 Hz will be: 

The correct answer is
1.75 kW

Understanding Core Loss in Silicon Steel

Core loss in magnetic materials like silicon steel is a significant factor in the efficiency of electrical machines and transformers. This loss represents the energy dissipated as heat within the core material when subjected to a varying magnetic field. It primarily consists of two components: hysteresis loss and eddy current loss.

Components of Core Loss

  • Hysteresis Loss ($\text{P}_{\text{h}}$): This loss is due to the energy required to repeatedly magnetize and demagnetize the core material as the magnetic field alternates. At a constant maximum flux density ($\text{B}_{\text{max}}$), the hysteresis loss is proportional to the frequency ($\text{f}$) of the alternating magnetic field. Mathematically, this can be expressed as $\text{P}_{\text{h}} = \text{K}_{\text{h}} \text{f}$, where $\text{K}_{\text{h}}$ is a constant that depends on the material properties and volume, and $\text{B}_{\text{max}}$.
  • Eddy Current Loss ($\text{P}_{\text{e}}$): This loss is caused by the circulating currents induced within the core material by the changing magnetic flux. These induced currents are called eddy currents. At a constant maximum flux density ($\text{B}_{\text{max}}$), the eddy current loss is proportional to the square of the frequency ($\text{f}^{\text{2}}$) and the square of the lamination thickness. Mathematically, this can be expressed as $\text{P}_{\text{e}} = \text{K}_{\text{e}} \text{f}^{\text{2}}$, where $\text{K}_{\text{e}}$ is a constant that depends on the material properties, volume, lamination thickness, and $\text{B}_{\text{max}}$.

The total core loss ($\text{P}_{\text{c}}$) is the sum of the hysteresis loss and the eddy current loss:

$\text{P}_{\text{c}} = \text{P}_{\text{h}} + \text{P}_{\text{e}}$

Given that the flux density is kept constant, we can write the total core loss as:

$\text{P}_{\text{c}} = \text{K}_{\text{h}} \text{f} + \text{K}_{\text{e}} \text{f}^{\text{2}}$

Dividing the total core loss by the frequency, we get:

$\frac{\text{P}_{\text{c}}}{\text{f}} = \text{K}_{\text{h}} + \text{K}_{\text{e}} \text{f}$

This equation shows a linear relationship between $\text{P}_{\text{c}}/\text{f}$ and $\text{f}$, with $\text{K}_{\text{h}}$ being the intercept and $\text{K}_{\text{e}}$ being the slope.

Solving the Problem

We are given two scenarios for the core loss in the specimen of silicon steel at constant flux density:

  1. At frequency $\text{f}_{\text{1}} = 50$ Hz, the total core loss $\text{P}_{\text{c1}} = 1500$ W.
  2. At frequency $\text{f}_{\text{2}} = 75$ Hz, the total core loss $\text{P}_{\text{c2}} = 3000$ W.

Using the formula $\frac{\text{P}_{\text{c}}}{\text{f}} = \text{K}_{\text{h}} + \text{K}_{\text{e}} \text{f}$, we can set up two equations:

For $\text{f}_{\text{1}} = 50$ Hz:

$\frac{1500}{50} = \text{K}_{\text{h}} + \text{K}_{\text{e}} \times 50$

$30 = \text{K}_{\text{h}} + 50 \text{K}_{\text{e}}$ (Equation 1)

For $\text{f}_{\text{2}} = 75$ Hz:

$\frac{3000}{75} = \text{K}_{\text{h}} + \text{K}_{\text{e}} \times 75$

$40 = \text{K}_{\text{h}} + 75 \text{K}_{\text{e}}$ (Equation 2)

Now we have a system of two linear equations with two unknowns, $\text{K}_{\text{h}}$ and $\text{K}_{\text{e}}$. We can solve this system.

Subtract Equation 1 from Equation 2:

$(40 - 30) = (\text{K}_{\text{h}} - \text{K}_{\text{h}}) + (75 \text{K}_{\text{e}} - 50 \text{K}_{\text{e}})$

$10 = 0 + 25 \text{K}_{\text{e}}$

$10 = 25 \text{K}_{\text{e}}$

Solving for $\text{K}_{\text{e}}$:

$\text{K}_{\text{e}} = \frac{10}{25} = 0.4$

Now substitute the value of $\text{K}_{\text{e}}$ into Equation 1 to find $\text{K}_{\text{h}}$:

$30 = \text{K}_{\text{h}} + 50 \times 0.4$

$30 = \text{K}_{\text{h}} + 20$

Solving for $\text{K}_{\text{h}}$:

$\text{K}_{\text{h}} = 30 - 20 = 10$

So, the core loss equation for this specimen at constant flux density is $\text{P}_{\text{c}} = 10 \text{f} + 0.4 \text{f}^{\text{2}}$.

We need to find the eddy current loss at 75 Hz. The formula for eddy current loss is $\text{P}_{\text{e}} = \text{K}_{\text{e}} \text{f}^{\text{2}}$.

At $\text{f} = 75$ Hz, the eddy current loss $\text{P}_{\text{e75}}$ is:

$\text{P}_{\text{e75}} = \text{K}_{\text{e}} \times (75)^{\text{2}}$

$\text{P}_{\text{e75}} = 0.4 \times (75 \times 75)$

$\text{P}_{\text{e75}} = 0.4 \times 5625$

$\text{P}_{\text{e75}} = 2250$ W

To express this in kilowatts (kW), we divide by 1000:

$\text{P}_{\text{e75}} = \frac{2250}{1000}$ kW $= 2.25$ kW

Thus, the eddy current loss at 75 Hz is 2.25 kW.

Summary of Calculation Steps

  1. Identify the components of core loss: hysteresis loss ($\text{K}_{\text{h}} \text{f}$) and eddy current loss ($\text{K}_{\text{e}} \text{f}^{\text{2}}$).
  2. Write the total core loss equation: $\text{P}_{\text{c}} = \text{K}_{\text{h}} \text{f} + \text{K}_{\text{e}} \text{f}^{\text{2}}$.
  3. Use the given data points ($\text{P}_{\text{c}}$, $\text{f}$) at constant flux density to form two equations for the unknowns $\text{K}_{\text{h}}$ and $\text{K}_{\text{e}}$.
  4. Solve the system of equations to find the values of $\text{K}_{\text{h}}$ and $\text{K}_{\text{e}}$.
  5. Use the calculated $\text{K}_{\text{e}}$ value to find the eddy current loss ($\text{P}_{\text{e}} = \text{K}_{\text{e}} \text{f}^{\text{2}}$) at the required frequency (75 Hz).
  6. Convert the result to kilowatts if necessary.
Frequency ($\text{f}$) Total Core Loss ($\text{P}_{\text{c}}$) $\text{P}_{\text{c}}/\text{f}$ Equation
50 Hz 1500 W $1500/50 = 30$ $30 = \text{K}_{\text{h}} + 50 \text{K}_{\text{e}}$
75 Hz 3000 W $3000/75 = 40$ $40 = \text{K}_{\text{h}} + 75 \text{K}_{\text{e}}$

Calculated Constants Value
$\text{K}_{\text{h}}$ 10
$\text{K}_{\text{e}}$ 0.4

Loss Component Frequency Formula Value
Eddy Current Loss 75 Hz $\text{P}_{\text{e}} = \text{K}_{\text{e}} \text{f}^{\text{2}}$ $0.4 \times (75)^2 = 2250$ W = 2.25 kW

The eddy current loss at 75 Hz is 2.25 kW.

Revision Table: Core Loss Components and Frequency Dependence

Loss Type Dependence on Frequency ($\text{f}$) (at constant $\text{B}_{\text{max}}$) Dependence on Maximum Flux Density ($\text{B}_{\text{max}}$) Dependence on Lamination Thickness ($\text{t}$) Primary Cause
Hysteresis Loss $\propto \text{f}$ $\propto \text{B}_{\text{max}}^{\text{x}}$ (Steinmetz: x ≈ 1.6) Independent Reversal of magnetic domains
Eddy Current Loss $\propto \text{f}^{\text{2}}$ $\propto \text{B}_{\text{max}}^{\text{2}}$ $\propto \text{t}^{\text{2}}$ Induced circulating currents

Additional Information: Minimizing Core Losses in Silicon Steel

To improve the efficiency of devices using silicon steel cores, engineers try to minimize both hysteresis and eddy current losses:

  • Minimizing Hysteresis Loss: This is primarily achieved by using soft magnetic materials that have a narrow hysteresis loop, such as specialized grades of silicon steel. The material composition and grain structure are carefully controlled.
  • Minimizing Eddy Current Loss: This loss is significantly reduced by constructing the core from thin laminations or sheets of silicon steel, insulated from each other by a thin layer of varnish or oxide. This insulation prevents large circulating currents from forming. The thinner the laminations, the higher the resistance to eddy current flow and the lower the loss. Another technique for high-frequency applications is using ferrite cores or powdered iron cores, where the material itself has high resistivity.

Understanding how core losses vary with frequency and flux density is crucial for designing efficient electrical equipment operating at different frequencies, such as 50 Hz, 60 Hz, or higher frequencies in power electronics.

Was this answer helpful?

Important Questions from Miscellaneous-Engineering

  1. A well foundation of 6 m external diameter and of 5 m internal diameter is sunk to a depth of 15 m in a deep deposit of sand. If the average N value of sand is 20, the load that the well can carry by bearing alone will be nearly
  2. What is the maximum depth to which a trench of vertical sides can be excavated in a clay stratum with c = 50 kN/m², y = 16 kN/m³, β = 90°, ¢ = 0°, Fc = 1 and N = 0-261?

  3. Which one of the following is an example of reinforced earth wall?
  4. Which one of the following data is not required for design of a weir or a barrage?
  5. In case of design of a weir or a barrage by providing a higher afflux, the waterway and, therefore, the length of the weir can be reduced, but it will result in
Need Expert Advice?

Start Your Preparation with Prepp Mobile App

Download the app from Google Play & App Store
Download the app from Google Play & App Store
Prepp Mobile App