The reactive power component kVAR =
kW tan∅ and kVA sin∅
In alternating current (AC) circuits, power is not just a single value. It is composed of different components. We usually talk about three types of power:
The relationship between these three types of power can be visualized using the power triangle. This is a right-angled triangle where:
Using trigonometry on the power triangle, we can find expressions for Reactive Power (kVAR).
Let S be Apparent Power (kVA), P be Active Power (kW), and Q be Reactive Power (kVAR). The power triangle gives us:
\(S^2 = P^2 + Q^2\)
\(\cos \theta = \frac{P}{S}\)
\(\sin \theta = \frac{Q}{S}\)
\(\tan \theta = \frac{Q}{P}\)
From the trigonometric relationships, we can derive formulas for Reactive Power (Q or kVAR):
From \(\sin \theta = \frac{Q}{S}\), we can rearrange to solve for Q:
\(Q = S \sin \theta\)
In terms of units, this is:
\(\text{kVAR} = \text{kVA} \sin \theta\)
From \(\tan \theta = \frac{Q}{P}\), we can rearrange to solve for Q:
\(Q = P \tan \theta\)
In terms of units, this is:
\(\text{kVAR} = \text{kW} \tan \theta\)
Both formulas, \(\text{kVA} \sin \theta\) and \(\text{kW} \tan \theta\), are valid ways to calculate Reactive Power (kVAR) depending on whether you know the apparent power (kVA) or the active power (kW) along with the power factor angle ∅.
Therefore, the reactive power component kVAR is equal to both kW tan∅ and kVA sin∅.
For a certain load, the true power is 100 W and the reactive power is 100 VAR. What is the apparent power?
What is the power factor of a alternating current circuit?
If the kVAR of an electric circuit is equal to ‘ZERO’, then the operating power factor of the same circuit is equal to:
What is the active power consumed by a motor if the total power is 400 VA with 0.5 power factor?
The power factor of a circuit is equal to