For a certain load, the true power is 100 W and the reactive power is 100 VAR. What is the apparent power?
141.4 VA
In alternating current (AC) circuits, power is described in three ways:
These three types of power are related through the power triangle, where true power and reactive power form the two legs of a right-angled triangle, and apparent power is the hypotenuse. The relationship is given by the Pythagorean theorem.
The relationship between true power (P), reactive power (Q), and apparent power (S) is fundamental in AC circuit analysis. It is expressed by the formula derived from the power triangle:
\[S^2 = P^2 + Q^2\]
Or, to find the apparent power (S):
\[S = \sqrt{P^2 + Q^2}\]
Here:
The question provides the following information:
We need to calculate the apparent power, \(S\). Using the formula \(S = \sqrt{P^2 + Q^2}\), we substitute the given values:
\[S = \sqrt{(100 \text{ W})^2 + (100 \text{ VAR})^2}\]
\[S = \sqrt{10000 + 10000}\]
\[S = \sqrt{20000}\]
To simplify \(\sqrt{20000}\), we can write it as \(\sqrt{2 \times 10000}\):
\[S = \sqrt{10000} \times \sqrt{2}\]
\[S = 100 \times \sqrt{2}\]
The value of \(\sqrt{2}\) is approximately 1.414.
\[S \approx 100 \times 1.414\]
\[S \approx 141.4 \text{ VA}\]
The calculated apparent power is approximately 141.4 VA. Let's compare this with the given options:
| Option | Apparent Power Value |
|---|---|
| 1 | 100 VA |
| 2 | 120 VA |
| 3 | 141.4 VA |
| 4 | 200 VA |
The calculated value of 141.4 VA matches Option 3.
| Power Type | Symbol | Unit | Description | Relationship |
|---|---|---|---|---|
| True Power | P | Watts (W) | Actual power used by the load for work (dissipated in resistance) | \(P = V_{rms} I_{rms} \cos(\phi)\) |
| Reactive Power | Q | Volt-Ampere Reactive (VAR) | Power exchanged between source and reactive components (inductors/capacitors) | \(Q = V_{rms} I_{rms} \sin(\phi)\) |
| Apparent Power | S | Volt-Ampere (VA) | Total power delivered from the source (vector sum of P and Q) | \(S = V_{rms} I_{rms}\), \(S = \sqrt{P^2 + Q^2}\) |
The power factor (PF) is another important concept in AC circuits. It is defined as the ratio of true power to apparent power:
\[\text{Power Factor} = \frac{P}{S} = \cos(\phi)\]
where \(\phi\) is the phase angle between the voltage and current. The power factor indicates how effectively the apparent power delivered to the load is being converted into useful work (true power). A power factor close to 1 (or unity) indicates efficient power usage, while a low power factor indicates that a significant portion of the apparent power is reactive power, which increases losses in the system.
In this specific problem, with \(P=100\) W and \(S \approx 141.4\) VA, the power factor would be:
\[\text{PF} = \frac{100}{141.4} \approx 0.707\]
This value corresponds to a phase angle \(\phi = \arccos(0.707)\), which is approximately 45 degrees. Since P and Q are equal, this represents a load with equal resistance and reactance (or a load with a total impedance angle of 45 degrees).