The core loss of a single phase, 230/115 V, 50Hz power transformer is measured from 230 V side by feeding the primary (230 V side) from a variable voltage variable frequency source while keeping the secondary open circuited. The core loss is measured to be 1050 W for 230 V, 50 Hz input. The core loss is gain measured to be 500 W for 138 V, 30 Hz input. The hysteresis and eddy current losses of the transformer for 230 V, 50 Hz input are respectively
508 W and 542 W
In any transformer, when alternating current flows through the primary winding, it creates a changing magnetic flux in the core. This alternating flux causes energy losses within the iron core, collectively known as core losses or iron losses. These losses are crucial as they affect the transformer's efficiency. Core losses consist of two main components:
The total core loss ($P_{core}$) is the sum of these two components: $P_{core} = P_h + P_e$.
We are provided with core loss measurements under two different operating conditions:
| Operating Condition | Voltage (V) | Frequency (Hz) | Measured Core Loss ($P_{core}$) (W) |
|---|---|---|---|
| 1 | 230 | 50 | 1050 |
| 2 | 138 | 30 | 500 |
The maximum flux density ($B_m$) in the transformer core is related to the applied voltage ($V$) and frequency ($f$) by the approximate formula $V \approx 4.44 f N K \Phi_m$, where $\Phi_m$ is related to $B_m$. Therefore, we can infer that $B_m$ is approximately proportional to the ratio $\frac{V}{f}$. Let's check this ratio for the given conditions:
Since the ratio $\frac{V}{f}$ is identical (4.6) for both test conditions, it indicates that the maximum flux density ($B_m$) in the transformer core remains constant during these two measurements.
The standard empirical relationships for core losses are:
Because we have established that $B_m$ is constant in our given scenarios, we can simplify these relationships by combining the constants:
The total core loss is the sum of these two components: $P_{core} = P_h + P_e = A f + B f^2$.
Using the data provided, we can establish a system of two linear equations:
We now solve the system of equations for the constants $A$ and $B$. The equations are:
1) $1050 = 50A + 2500B$
2) $500 = 30A + 900B$
To simplify, we can divide Equation 1 by 50 and Equation 2 by 10:
1') $21 = A + 50B$
2') $50 = 3A + 90B$
From Equation 1', let's express $A$ in terms of $B$: $A = 21 - 50B$
Now, substitute this expression for $A$ into Equation 2': $50 = 3(21 - 50B) + 90B$ $50 = 63 - 150B + 90B$ $50 = 63 - 60B$
Rearrange to solve for $B$: $60B = 63 - 50$ $60B = 13$ $B = \frac{13}{60}$
Substitute the value of $B$ back into the expression for $A$: $A = 21 - 50B = 21 - 50 \left(\frac{13}{60}\right)$ $A = 21 - \frac{5 \times 13}{6}$ $A = 21 - \frac{65}{6}$ $A = \frac{126}{6} - \frac{65}{6}$ $A = \frac{61}{6}$
With the constants $A = \frac{61}{6}$ and $B = \frac{13}{60}$, we can now calculate the hysteresis and eddy current losses for the specified input condition (230 V, 50 Hz).
Hysteresis Loss ($P_h$): $P_h = A f = \frac{61}{6} \times 50$ $P_h = \frac{3050}{6} = \frac{1525}{3}$ $P_h \approx 508.33 \text{ W}$
Eddy Current Loss ($P_e$): $P_e = B f^2 = \frac{13}{60} \times (50)^2$ $P_e = \frac{13}{60} \times 2500$ $P_e = \frac{13 \times 250}{6} = \frac{3250}{6} = \frac{1625}{3}$ $P_e \approx 541.67 \text{ W}$
The calculated hysteresis loss is approximately 508.33 W, and the eddy current loss is approximately 541.67 W. These values align closely with the option stating 508 W and 542 W.