Question

As per IS 456 : 2000, the minimum beam width required for a reinforced concrete beam, for 2 hours of fire exposure is:

The correct answer is

200 mm

Understanding IS 456:2000 Fire Resistance Requirements

The question asks about the minimum width required for a reinforced concrete beam according to IS 456:2000, specifically for a fire exposure duration of 2 hours. Concrete structures are designed not only for strength and serviceability but also for fire resistance to ensure the safety of occupants and prevent structural collapse during a fire event.

IS 456:2000 is the Indian Standard Code of Practice for Plain and Reinforced Concrete. It provides guidelines for various aspects of concrete design and construction, including provisions related to fire resistance.

Minimum Beam Width for Fire Resistance as per IS 456:2000

Annex A of IS 456:2000 deals with the Fire Resistance of Concrete Structures. This annex provides minimum dimensions for concrete members like beams, slabs, columns, and walls, along with minimum cover requirements, to achieve specific periods of fire resistance.

Table A.1 in IS 456:2000 provides the minimum dimensions of flexural members (like beams) and compression members (like columns) to achieve fire resistance ratings from 0.5 hours up to 4 hours.

Let's look at the requirements for flexural members (beams) based on the desired fire resistance period:

Fire Resistance (minutes) Fire Resistance (hours) Minimum Beam Width (mm)
30 0.5 80
60 1 120
90 1.5 150
120 2 200
180 3 200
240 4 240

According to this table from IS 456:2000, for a fire resistance period of 120 minutes (which is equal to 2 hours), the minimum required width for a reinforced concrete beam is 200 mm.

Detailed Analysis of Options

Now let's compare the options provided with the requirement from IS 456:2000 for 2 hours of fire exposure:

  • Option 1: 250 mm. This is greater than the minimum required 200 mm.
  • Option 2: 200 mm. This exactly matches the minimum requirement from the code for 2 hours.
  • Option 3: 300 mm. This is greater than the minimum required 200 mm.
  • Option 4: 150 mm. This is less than the minimum required 200 mm for 2 hours fire resistance. According to the table, 150 mm is the minimum width for 1.5 hours fire resistance.

Therefore, the minimum beam width required for a reinforced concrete beam for 2 hours of fire exposure, as per IS 456:2000, is 200 mm.

Revision Table: Key Dimensions for Fire Resistance

Fire Resistance Duration Minimum Reinforced Concrete Beam Width (IS 456:2000)
0.5 hours (30 min) 80 mm
1 hour (60 min) 120 mm
1.5 hours (90 min) 150 mm
2 hours (120 min) 200 mm
3 hours (180 min) 200 mm
4 hours (240 min) 240 mm

Additional Information on Concrete Fire Resistance

Fire resistance of concrete members depends on several factors, including:

  • Minimum Dimensions: As seen in the table, minimum width and depth (not shown here but also specified in the code) are crucial. Larger dimensions generally provide better fire resistance.
  • Concrete Cover: Adequate concrete cover to the reinforcement bars is essential. The cover protects the steel from reaching critical temperatures quickly, which would cause it to lose strength and buckle. IS 456:2000 also specifies minimum cover requirements for fire resistance in Table A.1.
  • Aggregate Type: The type of aggregate used in the concrete mix affects its performance under high temperatures. For example, concrete made with siliceous aggregates might spall more readily than concrete made with calcareous aggregates.
  • Member Type: Beams, slabs, columns, and walls have different fire resistance characteristics and thus different minimum dimensional requirements.
  • Load Conditions: The load on the member during a fire can also influence its fire resistance.

Adhering to these minimum requirements in IS 456:2000 helps ensure that concrete structures can withstand fire for a specified duration, allowing for safe evacuation and reducing potential structural damage.

Was this answer helpful?

Important Questions from Introduction

  1. In a limit state method the maximum strain allowed in axial compression concrete of a beam as per IS code is:

  2. For a load test of flexural member, the load to be placed on a structure as per IS code shall be:

    Where DL: Dead Load; LL: Live Load

  3. Which one of the following represents relationship between characteristic strength (f ck ), mean strength (f m) and standard deviation (s) as per relevant codal provisions?

  4. If welded fabric is used in RC wall having diameter equal to 16mm; the minimum ratio of vertical and horizontal reinforcements, respectively, to gross concrete area shall be:

  5. Which of the following is not a cash crop ?
Need Expert Advice?

Start Your Preparation with Prepp Mobile App

Download the app from Google Play & App Store
Download the app from Google Play & App Store
Prepp Mobile App