As per IS 456 : 2000, the minimum beam width required for a reinforced concrete beam, for 2 hours of fire exposure is:
200 mm
The question asks about the minimum width required for a reinforced concrete beam according to IS 456:2000, specifically for a fire exposure duration of 2 hours. Concrete structures are designed not only for strength and serviceability but also for fire resistance to ensure the safety of occupants and prevent structural collapse during a fire event.
IS 456:2000 is the Indian Standard Code of Practice for Plain and Reinforced Concrete. It provides guidelines for various aspects of concrete design and construction, including provisions related to fire resistance.
Annex A of IS 456:2000 deals with the Fire Resistance of Concrete Structures. This annex provides minimum dimensions for concrete members like beams, slabs, columns, and walls, along with minimum cover requirements, to achieve specific periods of fire resistance.
Table A.1 in IS 456:2000 provides the minimum dimensions of flexural members (like beams) and compression members (like columns) to achieve fire resistance ratings from 0.5 hours up to 4 hours.
Let's look at the requirements for flexural members (beams) based on the desired fire resistance period:
| Fire Resistance (minutes) | Fire Resistance (hours) | Minimum Beam Width (mm) |
|---|---|---|
| 30 | 0.5 | 80 |
| 60 | 1 | 120 |
| 90 | 1.5 | 150 |
| 120 | 2 | 200 |
| 180 | 3 | 200 |
| 240 | 4 | 240 |
According to this table from IS 456:2000, for a fire resistance period of 120 minutes (which is equal to 2 hours), the minimum required width for a reinforced concrete beam is 200 mm.
Now let's compare the options provided with the requirement from IS 456:2000 for 2 hours of fire exposure:
Therefore, the minimum beam width required for a reinforced concrete beam for 2 hours of fire exposure, as per IS 456:2000, is 200 mm.
| Fire Resistance Duration | Minimum Reinforced Concrete Beam Width (IS 456:2000) |
|---|---|
| 0.5 hours (30 min) | 80 mm |
| 1 hour (60 min) | 120 mm |
| 1.5 hours (90 min) | 150 mm |
| 2 hours (120 min) | 200 mm |
| 3 hours (180 min) | 200 mm |
| 4 hours (240 min) | 240 mm |
Fire resistance of concrete members depends on several factors, including:
Adhering to these minimum requirements in IS 456:2000 helps ensure that concrete structures can withstand fire for a specified duration, allowing for safe evacuation and reducing potential structural damage.
In a limit state method the maximum strain allowed in axial compression concrete of a beam as per IS code is:
For a load test of flexural member, the load to be placed on a structure as per IS code shall be:
Where DL: Dead Load; LL: Live Load
Which one of the following represents relationship between characteristic strength (f ck ), mean strength (f m) and standard deviation (s) as per relevant codal provisions?
If welded fabric is used in RC wall having diameter equal to 16mm; the minimum ratio of vertical and horizontal reinforcements, respectively, to gross concrete area shall be: