Question

If welded fabric is used in RC wall having diameter equal to 16mm; the minimum ratio of vertical and horizontal reinforcements, respectively, to gross concrete area shall be:

The correct answer is

0.0012 and 0.002

RC Wall Reinforcement Ratios

When designing Reinforced Concrete (RC) walls, it is crucial to ensure a minimum amount of reinforcement. This minimum reinforcement helps in controlling cracks caused by shrinkage and temperature variations, and it also contributes significantly to the overall structural integrity and ductility of the wall. The specific requirements for these minimum reinforcement ratios are outlined in design codes, such as IS 456:2000 (Indian Standard Code of Practice for Plain and Reinforced Concrete).

The question focuses on an RC wall where welded fabric is used, with a bar diameter equal to 16mm. In reinforced concrete construction, welded fabric and bars with diameters like 16mm are typically classified as high yield strength deformed (HYSD) bars, which fall under the category of deformed bars as per IS 456:2000 provisions for minimum reinforcement.

Minimum Reinforcement as per IS 456:2000 for RC Walls

According to Clause 32.5.1 of IS 456:2000, the minimum ratios of reinforcement to the gross concrete area of the wall vary depending on whether plain bars (Fe 250) or deformed bars (Fe 415, Fe 500) are used.

  • For Vertical Reinforcement: The minimum ratio of vertical reinforcement to the gross cross-sectional area of the RC wall is:
    • \(0.0012\) when deformed bars (such as Fe 415 or Fe 500, which includes welded fabric) are used.
    • \(0.0015\) when plain bars (Fe 250) are used.
  • For Horizontal Reinforcement: The minimum ratio of horizontal reinforcement to the gross cross-sectional area of the RC wall is:
    • \(0.0020\) when deformed bars (including welded fabric) are used.
    • \(0.0025\) when plain bars are used.

Given that the question specifies welded fabric (which is considered a type of deformed bar) and a 16mm diameter, we apply the provisions for deformed bars.

Reinforcement Direction Type of Steel Bar Minimum Ratio to Gross Concrete Area
Vertical Reinforcement Deformed Bars (e.g., HYSD, Welded Fabric) 0.0012
Plain Bars 0.0015
Horizontal Reinforcement Deformed Bars (e.g., HYSD, Welded Fabric) 0.0020
Plain Bars 0.0025

Therefore, for an RC wall constructed using welded fabric (deformed bars):

  • The minimum ratio of vertical reinforcement to gross concrete area is \(0.0012\).
  • The minimum ratio of horizontal reinforcement to gross concrete area is \(0.0020\).

These values are essential for ensuring the durability and structural performance of the RC wall, preventing excessive cracking and contributing to overall stability.

Thus, the correct minimum ratios for vertical and horizontal reinforcements, respectively, to gross concrete area are \(0.0012\) and \(0.002\).

Was this answer helpful?

Important Questions from Introduction

  1. In a limit state method the maximum strain allowed in axial compression concrete of a beam as per IS code is:

  2. For a load test of flexural member, the load to be placed on a structure as per IS code shall be:

    Where DL: Dead Load; LL: Live Load

  3. Which one of the following represents relationship between characteristic strength (f ck ), mean strength (f m) and standard deviation (s) as per relevant codal provisions?

  4. Which of the following is not a cash crop ?
  5. Which of the following is a plantation type of crop?

Need Expert Advice?

Start Your Preparation with Prepp Mobile App

Download the app from Google Play & App Store
Download the app from Google Play & App Store
Prepp Mobile App