Understanding the voltage drop in a DC distributor is crucial for efficient power distribution. This solution details the calculation of the maximum voltage drop for a uniformly loaded 2-wire DC distributor fed from one end.
Distributor Parameters
The following parameters are provided for the DC distributor:
- Distributor Type: Uniform 2-wire DC distributor
- Length (\(L\)): 200 m
- Load Density (\(k\)): 2 A/m (This means 2 Amperes of current are drawn uniformly per meter length of the distributor)
- Resistance of Single Wire (\(r'\)): 0.3 \(\Omega\)/km
- Feeding Condition: The distributor is fed from one end.
Unit Conversions
To ensure consistency in units for accurate calculation, we first need to convert the given resistance from \(\Omega\)/km to \(\Omega\)/m:
- Resistance of single wire per meter (\(r'_{m}\)):
$$r'_{m} = \frac{0.3 \, \Omega/\text{km}}{1000 \, \text{m/km}} = 0.0003 \, \Omega/\text{m}$$
- In a 2-wire DC distributor, the current flows through both the outgoing and return wires. Therefore, we need to consider the total resistance per meter for both wires, which is double the resistance of a single wire per meter:
$$R_{m} = 2 \times r'_{m} = 2 \times 0.0003 \, \Omega/\text{m} = 0.0006 \, \Omega/\text{m}$$
Maximum Voltage Drop Formula
For a uniformly loaded DC distributor that is fed from one end, the maximum voltage drop typically occurs at the far end of the distributor. The formula used to calculate this maximum voltage drop (\(V_{drop}\)) is:
$$V_{drop} = \frac{R_{m} \times k \times L^2}{2}$$
Where:
- \(V_{drop}\) = Maximum voltage drop (measured in Volts, V)
- \(R_{m}\) = Resistance of both wires per unit length (measured in Ohms per meter, \(\Omega\)/m)
- \(k\) = Uniform load density (measured in Amperes per meter, A/m)
- \(L\) = Total length of the distributor (measured in meters, m)
Step-by-Step Calculation
Now, let's substitute the identified and converted values into the voltage drop formula to find the solution:
- Identify the values for calculation:
- Resistance of both wires per meter, \(R_{m} = 0.0006 \, \Omega/\text{m}\)
- Load density, \(k = 2 \, \text{A/m}\)
- Length of the distributor, \(L = 200 \, \text{m}\)
- Substitute these values into the formula:
$$V_{drop} = \frac{0.0006 \, \Omega/\text{m} \times 2 \, \text{A/m} \times (200 \, \text{m})^2}{2}$$
- Calculate the square of the length (\(L^2\)):
$$(200 \, \text{m})^2 = 40000 \, \text{m}^2$$
- Multiply the terms in the numerator:
$$0.0006 \times 2 \times 40000 = 0.0012 \times 40000 = 48$$
- Divide the result by 2 to get the maximum voltage drop:
$$V_{drop} = \frac{48}{2} = 24 \, \text{V}$$
Voltage Drop Result
Based on the calculations, the maximum voltage drop for the given 2-wire DC distributor, which is 200 m long and uniformly loaded with 2 A/m, with a single-wire resistance of 0.3 \(\Omega\)/km, is 24 V.