A simply supported beam AB has a clear span of 7 meter. The bending moment diagram (BMD) of the beam due to a single concentrated load is shown in the figure below.
The magnitude of the concentrated load in kN is __________.
To determine the magnitude of the concentrated load on the beam, we will use the maximum bending moment formula for a simply supported beam with a point load:
M = P × a × b / L
Where:
Rearranging the formula to solve for P:
P = M × L / (a × b)
Substitute the known values:
P = 36 kN-m × 7 m / (3 m × 4 m)
P = 252 kN-m / 12 m
P = 21 kN
The magnitude of the concentrated load is 21 kN. This value falls within the expected range of 21 to 21 kN, confirming the correctness of our solution.
A rectangular beam section of size 300 mm (width) X 500 mm (depth) is loaded with a shear force of 600 kN. The maximum shear stress on the section in N/mm² is ___________
A simply supported RCC beam of cross section $0.4 \text{ m} \times 0.6 \text{ m}$ covers a span of $8 \text{ m}$. It is subjected to a uniformly distributed load of $30 \text{ kN/m}$. If the unit weight of concrete is $24 \text{ kN/m}^3$, the tensile stress (in $N/mm^2$, rounded off to two decimal places) at the bottom of the beam at mid-span is______