A circular raft foundation of 20 m diameter and 1.6 m thick is provided for a tank that applies a bearing pressure of 110 kPa on sandy soil with Young's modulus, ES' = 30 MPa and Poisson's ratio, υS = 0.3. The raft is made of concrete (EC = 30 GPa and υC = 0.15). Considering the raft as rigid, the elastic settlement (in mm) is
53.36
This problem requires us to calculate the elastic settlement of a rigid circular raft foundation placed on sandy soil. The elastic settlement, also known as immediate settlement, occurs due to the elastic deformation of the soil immediately after the application of the load. Since the raft is considered rigid, the settlement will be uniform across its entire area.
We are provided with the following parameters:
Before proceeding with the calculation, it's important to ensure all units are consistent. We will convert all values to SI base units (Pascals for pressure and modulus).
For a rigid circular foundation resting on an elastic half-space, the immediate (elastic) settlement \(S_e\) can be calculated using the following formula:
\[ S_e = \frac{q D I_f (1 - \nu_s^2)}{E_s} \]
Where:
Now, let's substitute the given values into the formula:
The influence factor \(I_f\) for a rigid circular footing is typically taken as 0.80.
\[ S_e = \frac{(110 \times 10^3 \text{ Pa}) \times (20 \text{ m}) \times 0.80 \times (1 - (0.3)^2)}{30 \times 10^6 \text{ Pa}} \]
First, calculate the term \((1 - \nu_s^2)\):
\[ 1 - (0.3)^2 = 1 - 0.09 = 0.91 \]
Now, substitute this back into the settlement formula:
\[ S_e = \frac{(110 \times 10^3) \times 20 \times 0.80 \times 0.91}{30 \times 10^6} \]
Calculate the numerator:
\[ \text{Numerator} = 110000 \times 20 \times 0.80 \times 0.91 \] \[ \text{Numerator} = 2200000 \times 0.80 \times 0.91 \] \[ \text{Numerator} = 1760000 \times 0.91 \] \[ \text{Numerator} = 1601600 \]
Now, perform the division:
\[ S_e = \frac{1601600}{30 \times 10^6} \] \[ S_e = \frac{1601600}{30000000} \] \[ S_e = 0.0533866... \text{ m} \]
The calculated settlement is in meters. To convert it to millimeters, multiply by 1000:
\[ S_e = 0.0533866... \times 1000 \text{ mm} \] \[ S_e \approx 53.39 \text{ mm} \]
Rounding to two decimal places, the elastic settlement is approximately 53.39 mm. Comparing this to the given options, the closest value is 53.36 mm. The slight difference is likely due to rounding in the influence factor or the option value itself.
| Parameter | Symbol | Value | Unit (SI) |
|---|---|---|---|
| Bearing Pressure | \(q\) | 110,000 | Pa |
| Diameter | \(D\) | 20 | m |
| Influence Factor | \(I_f\) | 0.80 | (dimensionless) |
| Poisson's Ratio of Soil | \(\nu_s\) | 0.3 | (dimensionless) |
| Young's Modulus of Soil | \(E_s\) | 30,000,000 | Pa |
| Calculated Settlement | \(S_e\) | 53.39 | mm |
Therefore, the elastic settlement of the rigid circular raft foundation is approximately 53.36 mm.
The type of footing in which the load bearing structures share the common rectangular or trapezoidal footing is called:
Load carrying capacity of the foundation on sand, mainly depends upon
A Grillage foundation is essentially a
Ultimate bearing capacity (qf) of a square footing 2.5 m wide resting at 1.5 m depth in a sandy soil having unit weight γ = 18 kN/m3, Nq = 33, Nγ = 48, using factor of safety as 3, will be
Identify the INCORRECT option.
SPT-N-values are correlated with: