Question

Which of the following can cause voltage sags?

The correct answer is

Single line-to-ground fault

Understanding Causes of Voltage Sags

A voltage sag, also known as a voltage dip, is a short-term reduction in the RMS voltage level. It's a common power quality issue that can affect sensitive electronic equipment. Sags typically last from 0.5 cycles to 1 minute and result in a voltage reduction to between 10% and 90% of the nominal voltage.

Analysis of Options Causing Voltage Sags

Let's analyze each option to determine which event causes voltage sags:

  • Option 1 Analysis: Voltage increase of the unfaulted phases during a single line-to-ground fault

    During a single line-to-ground fault, the voltage on the unfaulted phases typically decreases, not increases. This reduction is caused by the flow of fault current through the system's impedance. An increase in voltage on the unfaulted phases would indicate a voltage swell, not a sag. Therefore, this statement is incorrect as a cause for voltage sags.

  • Option 2 Analysis: Single line-to-ground fault

    A single line-to-ground fault occurs when one phase conductor accidentally contacts the ground. This creates a low-impedance path, causing a large fault current to flow. The flow of this current through the system's inherent impedance leads to a significant voltage drop, resulting in a voltage sag. The voltage level decreases considerably, especially on the faulted phase, and can impact adjacent phases depending on the fault characteristics and system grounding. This is a primary cause of voltage sags.

  • Option 3 Analysis: Switching off of a large load

    When a large load is switched off, the total power demand on the system decreases. This reduction in demand causes less current to flow through the system impedances. Consequently, the voltage drop across these impedances decreases, leading to a rise in the overall system voltage. This phenomenon is known as a voltage swell, not a voltage sag.

  • Option 4 Analysis: Energising a capacitor bank

    Capacitor banks are used to supply reactive power to the system. When a capacitor bank is switched on (energised), it injects reactive power, increasing the overall voltage level, particularly on lightly loaded systems. This injection of reactive power typically causes a voltage swell, similar to switching off a large load, rather than a voltage sag.

  • Option 5 Analysis: Empty Option

    This option is empty and therefore cannot be evaluated as a cause for voltage sags.

Conclusion on Voltage Sag Causes

Based on the analysis, a single line-to-ground fault is a direct cause of voltage sags due to the significant voltage drop created by the large fault current flowing through the system impedance.

Was this answer helpful?

Important Questions from Voltage Control

  1. Which component(s) is/are required to obtain a proportional DC voltage for a voltage sensing relay?

  2. Shunt reactors are sometimes used in high voltage transmission system to

  3. The complex power consumed by a constant – voltage load is given by (P1 + jQ1), Where, 1 kW ≤ P1 ≤ 1.5 kW and 0.5 kVAR ≤ Q1 ≤ 1 kVAR.

    A compensating shunt capacitor is chosen such that |Q| ≤ 0.25 kVAR, where Q is the net reactive power consumed by the capacitor – load combination. The reactive power (in kVAR) supplied by the capacitor is__________.
  4. For enhancing the power transmission in along EHV transmission line, the most preferred method is to connect a

  5. Which of the following is the function of static var system in EHV transmission?

Need Expert Advice?

Start Your Preparation with Prepp Mobile App

Download the app from Google Play & App Store
Download the app from Google Play & App Store
Prepp Mobile App