All Exams Test series for 1 year @ ₹349 only
Question

What are the values of positive constant ($K_p$), velocity constant ($K_v$) and acceleration constant ($K_a$) for a type '0' unity feedback system which has the transfer function $G(s) = \frac{1000(s+8)}{(s+7)(s+9)}$?

The correct answer is
$K_p = 127; K_v = 0; K_a = 0$

Understanding Steady-State Error Constants

For a unity feedback system, the steady-state error constants describe the system's response to different types of inputs at steady state. These constants are calculated from the open-loop transfer function $G(s)$.

The given open-loop transfer function is:

$ G(s) = \frac{1000(s+8)}{(s+7)(s+9)} $

The system is specified as type '0', meaning there are no poles at the origin ($s=0$) in the transfer function $G(s)$.

Calculating Positional Error Constant (Kp)

The positional error constant, $K_p$, is calculated as the limit of $G(s)$ as $s$ approaches 0:

$ K_p = \lim_{s \to 0} G(s) $

Substituting the given $G(s)$:

$ K_p = \lim_{s \to 0} \frac{1000(s+8)}{(s+7)(s+9)} $

$ K_p = \frac{1000(0+8)}{(0+7)(0+9)} = \frac{1000 \times 8}{7 \times 9} = \frac{8000}{63} $

$ K_p \approx 126.98 \approx 127 $

Calculating Velocity Error Constant (Kv)

The velocity error constant, $K_v$, is calculated as the limit of $s \cdot G(s)$ as $s$ approaches 0:

$ K_v = \lim_{s \to 0} s \cdot G(s) $

$ K_v = \lim_{s \to 0} s \cdot \frac{1000(s+8)}{(s+7)(s+9)} $

Since the transfer function $G(s)$ does not have a pole at $s=0$ (it's a type '0' system), the limit becomes:

$ K_v = 0 \cdot \frac{1000(0+8)}{(0+7)(0+9)} = 0 $

Calculating Acceleration Error Constant (Ka)

The acceleration error constant, $K_a$, is calculated as the limit of $s^2 \cdot G(s)$ as $s$ approaches 0:

$ K_a = \lim_{s \to 0} s^2 \cdot G(s) $

$ K_a = \lim_{s \to 0} s^2 \cdot \frac{1000(s+8)}{(s+7)(s+9)} $

Similar to $K_v$, because $G(s)$ is type '0', the limit becomes:

$ K_a = 0^2 \cdot \frac{1000(0+8)}{(0+7)(0+9)} = 0 $

Summary of Constants

The calculated values for the steady-state error constants are:

  • $K_p \approx 127$
  • $K_v = 0$
  • $K_a = 0$

Therefore, the correct option is $K_p = 127; K_v = 0; K_a = 0$.

Was this answer helpful?

Important Questions from Steady State Error

  1. The steady-state error due to unit step input to a type-1 system is:

  2. With reference to the error analysis of the control systems, the term 'acceleration error constant' stands for:

  3. Which one of the following coefficient is associated with Unit Ramp function?

  4. If the output of the system at steady state does not agree with the input, then the system is said to have _________ which determines the _________ of the system.

  5. A unity negative feedback closed loop system has a plant with the transfer function \(G(s) = \dfrac{1}{s^2 + 2s + 2}\) and a controller Ge(s) in the feedforward path. For a unit step input, the transfer function of the controller that gives minimum steady slate error is

Need Expert Advice?

Start Your Preparation with Prepp Mobile App

Download the app from Google Play & App Store
Download the app from Google Play & App Store
Prepp Mobile App