Two synchronous generators G1 and G2 rated 200 MW and 400 MW respectively are operated in parallel to supply a total load of 300 MW. If the governors in both the machines are set to a droop of 4%, what would be the individual power supplied by each generator?
This problem requires us to determine the individual power output of two synchronous generators connected in parallel. We are given their power ratings, the total load they are supplying, and the governor droop setting for both machines.
When synchronous generators operate in parallel, their governors regulate their power output based on the system frequency. The governor droop characteristic determines how much the power output changes for a given change in frequency. A droop setting means that as the load increases, the frequency typically decreases (or vice versa). Crucially, when multiple generators with the same droop percentage are synchronized and operating in parallel, they will naturally share the total system load in proportion to their individual capacity ratings. This ensures stable operation and appropriate distribution of the demand among the available resources.
We have the following information provided:
| Generator | Rating (MW) |
|---|---|
| G1 | 200 |
| G2 | 400 |
Total Load Supplied by both generators: $300 \text{ MW}$
Governor Droop Setting for both G1 and G2: $4\%$
Since both generators share the same governor droop setting (4%), the total load of $300 \text{ MW}$ will be divided between them proportionally based on their installed capacities. First, we calculate the total capacity of the combined system.
The total capacity is the sum of the individual ratings of the generators operating in parallel.
Total Capacity ($C_{total}$) = Rating$_{G1}$ + Rating$_{G2}$
Using mathematical notation:
$$C_{total} = R_1 + R_2$$
Substituting the given values:
$$C_{total} = 200 \text{ MW} + 400 \text{ MW}$$
$$C_{total} = 600 \text{ MW}$$
Generator G1 will supply a portion of the total load that is equal to its rating relative to the total system capacity, multiplied by the total load.
Power Supplied by G1 ($P_{G1}$) = Total Load $\times \frac{\text{Rating}_{G1}}{\text{Total Capacity}}$
Using mathematical notation:
$$P_{G1} = P_{load} \times \frac{R_1}{C_{total}}$$
Substituting the values:
$$P_{G1} = 300 \text{ MW} \times \frac{200 \text{ MW}}{600 \text{ MW}}$$
$$P_{G1} = 300 \text{ MW} \times \frac{1}{3}$$
$$P_{G1} = 100 \text{ MW}$$
Similarly, Generator G2 will supply a portion of the total load proportional to its rating relative to the total system capacity.
Power Supplied by G2 ($P_{G2}$) = Total Load $\times \frac{\text{Rating}_{G2}}{\text{Total Capacity}}$
Using mathematical notation:
$$P_{G2} = P_{load} \times \frac{R_2}{C_{total}}$$
Substituting the values:
$$P_{G2} = 300 \text{ MW} \times \frac{400 \text{ MW}}{600 \text{ MW}}$$
$$P_{G2} = 300 \text{ MW} \times \frac{2}{3}$$
$$P_{G2} = 200 \text{ MW}$$
After performing the calculations based on the principle of proportional load sharing due to identical governor droop settings, we find that Generator G1 supplies $100 \text{ MW}$ and Generator G2 supplies $200 \text{ MW}$.
Thus, the individual power supplied by each generator is:
G1 = 100 MW, G2 = 200 MW
Which component(s) is/are required to obtain a proportional DC voltage for a voltage sensing relay?
Shunt reactors are sometimes used in high voltage transmission system to
The complex power consumed by a constant – voltage load is given by (P1 + jQ1), Where, 1 kW ≤ P1 ≤ 1.5 kW and 0.5 kVAR ≤ Q1 ≤ 1 kVAR.
A compensating shunt capacitor is chosen such that |Q| ≤ 0.25 kVAR, where Q is the net reactive power consumed by the capacitor – load combination. The reactive power (in kVAR) supplied by the capacitor is__________.For enhancing the power transmission in along EHV transmission line, the most preferred method is to connect a
Which of the following is the function of static var system in EHV transmission?