To turn off the SCR, which of the following is done?
Reduce anode voltage to zero
The question asks about the correct method to turn off a Silicon Controlled Rectifier (SCR). An SCR is a type of thyristor, which is a semiconductor device primarily used for power control. It acts like a switch that can be turned on electronically, but it has a unique characteristic: once triggered into conduction, it remains ON even if the trigger signal is removed, as long as the current flowing through it (the anode current) is above a certain minimum level known as the holding current ($I_H$).
An SCR turns ON when it receives a positive gate pulse (relative to the cathode) while the anode is positive with respect to the cathode. After turn-on, the gate loses its control. To turn the SCR OFF, the anode current ($I_A$) must be reduced below the holding current ($I_H$). This can be achieved through two main methods: natural commutation (occurs in AC circuits when the voltage reverses) or forced commutation (using external circuitry to force the anode current to zero temporarily).
Let's examine why each option is correct or incorrect:
Therefore, reducing the anode voltage to zero is an effective way to ensure the anode current falls below the holding current, successfully turning the SCR OFF.