All Exams Test series for 1 year @ ₹349 only
Question

The heat loss from a fin is 6 W. The effectiveness and efficiency of the fin are 3 and 0.75 respectively. The heat loss from the fin (in W) keeping the entire fin surface at base temperature, is

The correct answer is

8

Solving Fin Heat Loss Problem with Efficiency

The problem provides information about the heat loss from a fin, its effectiveness, and its efficiency. We need to determine the heat loss from the fin if its entire surface were maintained at the base temperature.

We are given:

  • Actual heat loss from the fin ($Q_{fin}$) = 6 W
  • Effectiveness of the fin ($\epsilon$) = 3
  • Efficiency of the fin ($\eta$) = 0.75

The quantity we need to find is the heat loss from the fin if its entire surface were at the base temperature. This is often referred to as the ideal heat transfer rate, or the maximum possible heat transfer rate for the given fin area and temperature difference.

The efficiency of a fin is defined as the ratio of the actual heat transfer rate from the fin to the ideal heat transfer rate that would occur if the entire fin surface were at the base temperature.

Mathematically, fin efficiency ($\eta$) is expressed as:

\(\eta = \frac{\text{Actual heat loss from fin}}{\text{Heat loss from fin if entire surface were at base temperature}}\)

Let $Q_{ideal}$ be the heat loss from the fin if the entire surface were at the base temperature. The formula becomes:

\(\eta = \frac{Q_{fin}}{Q_{ideal}}\)

We are given $Q_{fin} = 6$ W and $\eta = 0.75$. We need to find $Q_{ideal}$.

We can rearrange the formula to solve for $Q_{ideal}$:

\(Q_{ideal} = \frac{Q_{fin}}{\eta}\)

Now, we substitute the given values into the rearranged formula:

\(Q_{ideal} = \frac{6 \text{ W}}{0.75}\)

To calculate this value:

\(Q_{ideal} = \frac{6}{0.75} = \frac{6}{3/4} = 6 \times \frac{4}{3} = \frac{24}{3} = 8 \text{ W}\)

Thus, the heat loss from the fin if its entire surface were kept at the base temperature is 8 W.

The effectiveness value (3) was provided but was not directly needed to solve for the ideal heat loss using the efficiency definition.

The final answer is 8 W.

Was this answer helpful?

Important Questions from Fins

  1. In an infinitely long fin, if the parameter m = \(\rm \sqrt{\frac{hP}{kA}} \) increases, the other parameters being maintained constant, then __________.

  2. For having the highest fin effectiveness, the fins should be _______.
  3. It is the appropriate that area of cross-section for a fin be

  4. Effectiveness of Infinitely long fin is given by

    (where, P = Fin parameter, K = Fin thermal conductivity, h = Convective heat transfer coefficient, Ac = Fin cross-section area)

  5. Fin ______ is termed as the ratio of the heat transfer rate of a fin to heat transfer rate without fin.

Need Expert Advice?

Start Your Preparation with Prepp Mobile App

Download the app from Google Play & App Store
Download the app from Google Play & App Store
Prepp Mobile App