The dry-bulb temperature of air in a room is $30 \ \degree C$. The Antoine equation for water is given as
$ln \ P^{sat} = 12.00 - \frac{4000}{T-40}$
where $T$ is the temperature in $K$ and $P^{sat}$ is the saturation vapor pressure in $bar$. The latent heat of vaporization of water is $2000 \ kJ \ kg^{-1}$, the humid heat is $1.0 \ kJ \ kg^{-1} \ K^{-1}$, and the molecular weights of air and water are $28 \ kg \ kmol^{-1}$ and $18 \ kg \ kmol^{-1}$, respectively. If the absolute humidity of air is $Y' \ kg$ moisture per $kg$ dry air, then for a wet-bulb depression of $9 \ \degree C$, $1000 \times Y' = $ _________ (rounded off to one decimal place).
This solution details the calculation of absolute humidity ($Y'$) using psychrometric principles, the Antoine equation for saturation vapor pressure, and an energy balance, given the dry-bulb temperature ($T_{db}$), wet-bulb depression ($\Delta T_{wb}$), humid heat ($C_{ph}$), and latent heat of vaporization ($h_{fg}$).
Dry-bulb temperature, $T_{db} = 30 \ \degree C$. Convert to Kelvin: $ T_{db\_K} = 30 + 273.15 = 303.15 \ K $. Wet-bulb depression, $\Delta T_{wb} = 9 \ \degree C$. Humid heat, $C_{ph} = 1.0 \ kJ \ kg^{-1} \ K^{-1}$. Latent heat of vaporization, $h_{fg} = 2000 \ kJ \ kg^{-1}$. Molecular weight ratio, $M_{water}/M_{air} = 18/28$. Standard atmospheric pressure is assumed: $P_{atm} = 1.01325 \ bar$.
$ T_{wb} = T_{db} - \Delta T_{wb} = 30 \ \degree C - 9 \ \degree C = 21 \ \degree C $. Convert to Kelvin: $ T_{wb\_K} = 21 + 273.15 = 294.15 \ K $.
Using the provided Antoine equation: $ P_{wb}^{sat} = \exp\left(12.00 - \frac{4000}{T_{wb\_K}-40}\right) $ $ P_{wb}^{sat} = \exp\left(12.00 - \frac{4000}{294.15-40}\right) $ $ P_{wb}^{sat} = \exp\left(12.00 - \frac{4000}{254.15}\right) $ $ P_{wb}^{sat} = \exp\left(12.00 - 15.7389\right) = \exp(-3.7389) \approx 0.02387 \ bar $.
$ Y'_{wb}^{sat} = \frac{M_{water}/M_{air} \times P_{wb}^{sat}}{P_{atm} - P_{wb}^{sat}} $ $ Y'_{wb}^{sat} = \frac{(18/28) \times 0.02387}{1.01325 - 0.02387} $ $ Y'_{wb}^{sat} = \frac{0.642857 \times 0.02387}{1.009383} \approx \frac{0.015329}{1.009383} \approx 0.015186 \ kg \ moisture/kg \ dry \ air $.
From the energy balance equation $ C_{ph} (T_{db} - T_{wb}) = h_{fg} (Y'_{wb}^{sat} - Y') $, we rearrange to solve for $Y'$: $ Y' = Y'_{wb}^{sat} - \frac{C_{ph} (T_{db} - T_{wb})}{h_{fg}} $ Substitute the known values: $ Y' = 0.015186 - \frac{1.0 \ kJ \ kg^{-1} \ K^{-1} \times (30 - 21) \ K}{2000 \ kJ \ kg^{-1}} $ $ Y' = 0.015186 - \frac{9}{2000} $ $ Y' = 0.015186 - 0.0045 $ $ Y' = 0.010686 \ kg \ moisture/kg \ dry \ air $.
The question asks for the value of $1000 \times Y'$. $ 1000 \times Y' = 1000 \times 0.010686 = 10.686 $. Rounding to one decimal place gives $10.7$.
| Temperature (in K) | 284 | 289 | 294 | 299 | 310 |
| Vapor pressure of water (in kPa) | 1.28 | 1.80 | 2.50 | 3.40 | 6.40 |
Consider moist air with absolute humidity of 0.02 (kg moisture)/(kg dry air) at 1 bar pressure. The vapour pressure of water is given by the equation
$\ln P^{sat} = 12 - \frac{4000}{T-40}$
where $P^{sat}$ is in bar and $T$ is in K. The molecular weight of water and dry air are 18 kg/kmol and 29 kg/kmol, respectively. The dew temperature of the moist air is ____________ °C (rounded off to the nearest integer).
Partially saturated air at 1 bar and $50 ^{\circ}C$ is contacted with water in an adiabatic saturator. The air is cooled and humidified to saturation, and exits at $25^{\circ}C$ with an absolute humidity of 0.02 kg water per kg dry air. Use latent heat of vaporization of water as 2450 kJ. $kg^{-1}$, and average specific heat capacity for dry air and water, respectively as 1.01 kJ.$kg^{-1}K^{-1}$ and 4.18 kJ. $kg^{-1}K^{-1}$. If the absolute humidity of air entering the adiabatic saturator is $H \times 10^{-3}$ kg water per kg dry air, the value of $H$ is ________ (rounded off to two decimal places).
The humidity of air at a dry-bulb temperature of $65^{\circ}C$ is $0.025 \; kg \; water/kg \; dry \; air$. The latent heat of vaporization of water at $0 ^{\circ}C$ is $2500 \; kJ/kg$. The psychrometric ratio of air is $0.95 \; kJ \; (kg \; dry \; air)^{-1} \; K^{-1}$. Considering $0 ^{\circ}C$ as reference temperature, the enthalpy of air (in kJ/kg) at its adiabatic saturation temperature of $35 ^{\circ}C$ is ________ (rounded off to two decimal places).