The direct axis and quadrature axis reactance of a salient pole alternator are 1.2 p.u and 1.0 p.u respectively. The armature resistance is negligible. If the alternator is delivering rated kVA at upf and at rated voltage then its power angle is

The correct answer is

45°

Rated voltage and current are both1 pu at unity power factor. For a salient-pole generator, tanδ=XqI/(V)=1·1/1=1. Hence δ=45°. Xd affects the required excitation, not this angle relation.