This solution details the calculation for the compressor power consumption required to freeze marine fishery products using a plate freezer. The process involves calculating the total heat to be removed from the product and then using the refrigeration system's COP to find the power input.
First, we extract the given parameters and calculate the masses of water and solids in the fishery products.
Given Data:
Calculated Masses:
The total heat ($Q_{total}$) to be removed is the sum of sensible heat during cooling phases and latent heat during freezing.
Heat removed to cool the fresh fish (water and solids) from $32^\circ C$ down to its freezing point of $-0.3^\circ C$.
Temperature difference: $\Delta T_1 = T_i - T_{fp} = 32^\circ C - (-0.3^\circ C) = 32.3^\circ C = 32.3$ K
Sensible heat ($Q_1$) = (Heat from water) + (Heat from solids)
$Q_1 = (m_w \times c_{pw} \times \Delta T_1) + (m_s \times c_{ps} \times \Delta T_1)$
$Q_1 = (850 \text{ kg} \times 4.2 \frac{kJ}{kg \cdot K} \times 32.3 \text{ K}) + (150 \text{ kg} \times 3.2 \frac{kJ}{kg \cdot K} \times 32.3 \text{ K})$
$Q_1 = 115749 \text{ kJ} + 15504 \text{ kJ} = 131253 \text{ kJ}$
Heat removed to freeze the water content at the constant freezing point of $-0.3^\circ C$.
Latent heat ($Q_2$) = $m_w \times L_w$
$Q_2 = 850 \text{ kg} \times 335 \frac{kJ}{kg} = 284750 \text{ kJ}$
Heat removed to cool the now frozen product (ice and solids) from $-0.3^\circ C$ down to the final temperature of $-18^\circ C$.
Temperature difference: $\Delta T_2 = T_{fp} - T_f = -0.3^\circ C - (-18^\circ C) = 17.7^\circ C = 17.7$ K
Sensible heat ($Q_3$) = (Heat from ice) + (Heat from frozen solids)
$Q_3 = (m_w \times c_{ice} \times \Delta T_2) + (m_s \times c_{ps,frozen} \times \Delta T_2)$
$Q_3 = (850 \text{ kg} \times 2.2 \frac{kJ}{kg \cdot K} \times 17.7 \text{ K}) + (150 \text{ kg} \times 1.8 \frac{kJ}{kg \cdot K} \times 17.7 \text{ K})$
$Q_3 = 33117 \text{ kJ} + 4783 \text{ kJ} = 37900 \text{ kJ}$
The total heat to be removed is the sum of the heat loads from the three stages.
$Q_{total} = Q_1 + Q_2 + Q_3$
$Q_{total} = 131253 \text{ kJ} + 284750 \text{ kJ} + 37900 \text{ kJ} = 453903 \text{ kJ}$
The refrigeration rate ($\dot{Q}_L$) is the total heat load divided by the specified freezing time.
Convert freezing time to seconds: $\Delta t = 0.5 \text{ hours} \times 3600 \frac{\text{seconds}}{\text{hour}} = 1800$ seconds
Refrigeration rate: $\dot{Q}_L = \frac{Q_{total}}{\Delta t}$
$\dot{Q}_L = \frac{453903 \text{ kJ}}{1800 \text{ s}} \approx 252.168 \text{ kW}$
The compressor power consumption ($\dot{W}_c$) is determined using the COP of the refrigeration cycle.
The relationship is: $COP = \frac{\text{Refrigeration Rate}}{\text{Compressor Power Consumption}} = \frac{\dot{Q}_L}{\dot{W}_c}$
Rearranging for power consumption: $\dot{W}_c = \frac{\dot{Q}_L}{COP}$
$\dot{W}_c = \frac{252.168 \text{ kW}}{3.66} \approx 68.898 \text{ kW}$
The calculated compressor power consumption is approximately $68.9$ kW, confirming the value lies between 68 and 69 kW.
In a plate freezer, the plate temperature is maintained at $-25 \ ^\circ C$. Latent heat of crystallization is $335 \, kJ \, kg^{-1}$, and the thermal conductivity and density of frozen meat are $1.25 \ W \, m^{-1} \, K^{-1}$ and $1060 \ kg \, m^{-3}$, respectively. Assuming freezing point of deboned meat at 85% water content on wet basis to be $0 \ ^\circ C$, the freezing time in minutes for 2 cm thick block of meat, kept between a pair of freezing plates, is ________.
A fish fillet of $5 \text{ mm}$ thickness having $85\%$ moisture (wet basis) is to be frozen using a plate freezer. The plates are at $-35 \text{ }^\circ C$ and the heat transfer coefficient between the fillet and the freezer plates can be assumed to be $2.0 \text{ W m}^{-2} \text{ K}^{-1}$. The initial freezing temperature of fish is $-2.5 \text{ }^\circ C$, latent heat of fusion is $330 \text{ kJ kg}^{-1}$, density of fish is $1100 \text{ kg m}^{-3}$ and thermal conductivity of frozen fish is $1.5 \text{ W m}^{-1} \text{ K}^{-1}$. The time required to freeze the fillet from the initial freezing temperature in hour(s) is_______
A contact plate freezer extracts thermal energy from a $24$ mm thick slab of boneless meat containing $85$% (w/w) water. Initially the slab is at the freezing point of meat, that is $272.5$ K and corresponding latent heat of freezing is $335$ kJ kg$^{-1}$ water. The plate temperature of the freezer is assumed steady at $247.5$ K. Bulk density of the slab is $750$ kg m$^{-3}$. The thermal conductivity value for frozen meat is $1.5$ W m$^{-1}$ K$^{-1}$. The minimum duration required for complete freezing of the slab in seconds is _____________