All Exams Test series for 1 year @ ₹349 only
Question

For limit state design of RC beam consider following:

i) \(\left[ {\frac{{{f_y}}}{{{f_{ck}}}} = 0.36} \right]\)

ii) \(\left[ {\frac{{{A_{st}}}}{{bd}} = 4\% } \right]\)

iii) \(\left[ {\frac{{{x_{u\;max}}}}{d} = 0.48} \right]\)

Which one of the design criteria shall be applicable?

The correct answer is

Under reinforced section

RC Beam Design Criterion Explained

The question asks us to determine the applicable design criterion for an RC beam based on given parameters for limit state design. We need to compare the actual neutral axis depth ratio (\(x_u/d\)) with the maximum permissible neutral axis depth ratio (\(x_{u,max}/d\)).

Understanding RC Beam Sections

In the limit state design of reinforced concrete beams, sections are classified based on the relative positions of the actual neutral axis and the maximum permissible neutral axis depth:

  • Under-reinforced Section: This occurs when the actual neutral axis depth (\(x_u\)) is less than the maximum permissible neutral axis depth (\(x_{u,max}\)). In this type of section, the steel reinforcement reaches its yield stress before the concrete reaches its ultimate compressive strain. This failure is ductile, meaning it gives visible warning signs (large deflections) before collapse, which is generally preferred in design for safety.
  • Balanced Section: This is a theoretical condition where the steel reinforcement reaches its yield stress and the concrete reaches its ultimate compressive strain simultaneously. In this case, the actual neutral axis depth (\(x_u\)) is equal to the maximum permissible neutral axis depth (\(x_{u,max}\)).
  • Over-reinforced Section: This occurs when the actual neutral axis depth (\(x_u\)) is greater than the maximum permissible neutral axis depth (\(x_{u,max}\)). In this type of section, the concrete reaches its ultimate compressive strain before the steel reinforcement yields. This failure is brittle and sudden, providing little to no warning, and is therefore generally avoided in design.

Limit State Design Parameters

We are provided with the following parameters for the RC beam:

  • i) Ratio of yield strength of steel to characteristic compressive strength of concrete: \(\left[ {\frac{{{f_y}}}{{{f_{ck}}}} = 0.36} \right]\)
  • ii) Ratio of area of steel to effective area of beam: \(\left[ {\frac{{{A_{st}}}}{{bd}} = 4\% = 0.04} \right]\)
  • iii) Maximum permissible neutral axis depth ratio: \(\left[ {\frac{{{x_{u\;max}}}}{d} = 0.48} \right]\)

Calculating Actual Neutral Axis Depth Ratio (\(x_u/d\))

In limit state design, the actual neutral axis depth (\(x_u\)) for a rectangular section is determined by equating the total compressive force in concrete to the total tensile force in steel. The formula for the actual neutral axis depth ratio (\(x_u/d\)) is given by:

\[\frac{{{x_u}}}{d} = \frac{{0.87{f_y}{A_{st}}}}{{0.36{f_{ck}}bd}}\]

This formula can be rearranged to use the given ratios:

\[\frac{{{x_u}}}{d} = \frac{{0.87}}{{0.36}} \times \left( {\frac{{{f_y}}}{{{f_{ck}}}}} \right) \times \left( {\frac{{{A_{st}}}}{{bd}}} \right)\]

Now, let's substitute the given values into the formula:

  • \(\frac{{{f_y}}}{{{f_{ck}}}} = 0.36\)
  • \(\frac{{{A_{st}}}}{{bd}} = 0.04\)

So, the calculation for \(\frac{{{x_u}}}{d}\) is:

\[\frac{{{x_u}}}{d} = \frac{{0.87}}{{0.36}} \times 0.36 \times 0.04\]

\[\frac{{{x_u}}}{d} = 0.87 \times 0.04\]

\[\frac{{{x_u}}}{d} = 0.0348\]

Comparing Neutral Axis Depths

Now we compare the calculated actual neutral axis depth ratio (\(x_u/d\)) with the given maximum permissible neutral axis depth ratio (\(x_{u,max}/d\)).

  • Calculated \(\frac{{{x_u}}}{d} = 0.0348\)
  • Given \(\frac{{{x_{u\;max}}}}{d} = 0.48\)

Upon comparison, we observe that:

\[0.0348 < 0.48\]

This means that \(x_u < x_{u,max}\).

Determining Applicable Design Criterion

Since the actual neutral axis depth \(x_u\) is less than the maximum permissible neutral axis depth \(x_{u,max}\) (\(x_u < x_{u,max}\)), the RC beam section is an under-reinforced section.

Under-reinforced sections are preferred in design as they exhibit ductile failure, providing warning before collapse, which enhances the safety of the structure.

 

ConditionSection TypeFailure Mode
\(x_u < x_{u,max}\)Under-reinforcedDuctile (steel yields first)
\(x_u = x_{u,max}\)BalancedDuctile (steel yields & concrete crushes simultaneously)
\(x_u > x_{u,max}\)Over-reinforcedBrittle (concrete crushes first)

 


 

Was this answer helpful?

Important Questions from Beams and Slabs

  1. What should be the clear distance between the lateral restraint for continuous beams?

  2. On what does the thickness of slab primarily depend?

  3. In a doubly reinforced rectangular beam, bending stress induced in compression (i.e. concrete) and tension (i.e. steel) are σ ch and σ st , respectively. The depth of neutral axis is kd (where d is effective depth) from top compression face and modular ratio is m. Which one of the following represents correct combination in under reinforced beam?

  4. In a RC cantilever beam which is subjected to downward load, tension reinforcement needs be provided at:

  5. Which one of the following represents effective width of flange of T-beam?