For a specified input voltage and frequency, if the equivalent radius of the core of a transformer is reduced by half, the factor by which the number of turns in the primary should change to maintain the same no load current is
2
This question asks how the number of turns in a transformer's primary winding needs to change if the core's equivalent radius is halved, while keeping the input voltage, frequency, and the resulting no-load current constant. The no-load current in a transformer is primarily the magnetizing current, which is required to establish the magnetic flux in the core.
The no-load current ($ I_0 $) is mainly responsible for magnetizing the core. Its magnitude depends on the voltage ($ V $), frequency ($ f $), the number of turns ($ N $), and the magnetic properties of the core, specifically its reluctance ($ \mathcal{R} $).
The relationship can be approximated as:
The maximum flux ($ \Phi_m $) is determined by the applied voltage ($ V $) and frequency ($ f $) through the EMF equation: $ V \approx 4.44 f N \Phi_m $. For a constant voltage ($ V $) and frequency ($ f $), the required flux ($ \Phi_m $) remains constant, assuming the number of turns ($ N $) doesn't drastically change the required flux.
The reluctance ($ \mathcal{R} $) of the magnetic core is given by $ \mathcal{R} = \frac{l}{\mu A} $, where:
If the equivalent radius ($ r $) of the core is reduced by half ($ r' = r/2 $), we can assume the linear dimensions of the core scale proportionally.
Now, let's find the new reluctance ($ \mathcal{R}' $):
$ \mathcal{R}' = \frac{l'}{\mu A'} = \frac{l/2}{\mu (A/4)} = \frac{l}{\mu A} \times \frac{4}{2} = 2 \times \frac{l}{\mu A} = 2\mathcal{R} $
This means the reluctance of the core doubles when the equivalent radius is halved.
We need to maintain the same no-load current ($ I_0 $). Let the initial state be denoted by subscript 1 and the final state by subscript 2.
We are given:
Equating the expressions for $ I_0 $:
$ \frac{\mathcal{R}_1 \Phi_{m,1}}{N_{p,1}} = \frac{\mathcal{R}_2 \Phi_{m,2}}{N_{p,2}} $
Substitute the known relationships:
$ \frac{\mathcal{R}_1 \Phi_{m,1}}{N_{p,1}} = \frac{(2\mathcal{R}_1) \Phi_{m,1}}{N_{p,2}} $
Cancelling out $ \mathcal{R}_1 $ and $ \Phi_{m,1} $ from both sides:
$ \frac{1}{N_{p,1}} = \frac{2}{N_{p,2}} $
Rearranging to find the new number of turns ($ N_{p,2} $):
$ N_{p,2} = 2 N_{p,1} $
To maintain the same no-load current when the core's equivalent radius is halved (which doubles the core reluctance), the number of turns in the primary winding must be doubled. Therefore, the factor by which the number of turns should change is 2.
For a potential transformer the turns ratio is defined as the-
Which of the following is NOT an advantage of shell type transformers over core type transformers?
Ferrite cores are used in high frequency transformer, because it has:
With core type of transformers, the limbs are stepped so as to
Which part of the transformer is constructed by the L, I and E type of laminated steel?