For a room RTH = 100 kW, RSHF = 0.75, volume flow rate of air 100 m3/min and room humidity ratio =0.01 kg/kh d.a. What is supply air humidity ratio (kg/kg)?
0.005
Calculating Supply Air Humidity Ratio for HVAC System
This problem requires us to find the humidity ratio of the supply air ($\omega_S$) given the room conditions and cooling load.
We are provided with the following information for the room:
The Room Total Heat (RTH) is the sum of Room Sensible Heat (RSH) and Room Latent Heat (RLH).
$$RTH = RSH + RLH$$
The Room Sensible Heat Factor (RSHF) relates the sensible heat to the total heat:
$$RSHF = \frac{RSH}{RTH}$$
Using the given RSHF and RTH, we can calculate RSH:
$$RSH = RSHF \times RTH$$
$$RSH = 0.75 \times 100 \text{ kW}$$
$$RSH = 75 \text{ kW}$$
Now, we can find the Room Latent Heat (RLH):
$$RLH = RTH - RSH$$
$$RLH = 100 \text{ kW} - 75 \text{ kW}$$
$$RLH = 25 \text{ kW}$$
The latent heat removed from the room is related to the mass flow rate of air and the change in humidity ratio between the room air and the supply air. First, we need to find the mass flow rate of dry air ($\dot{m}_a$).
The volume flow rate is given as 100 m³/min. We convert this to m³/s:
$$V = 100 \frac{\text{m}^3}{\text{min}} \times \frac{1 \text{ min}}{60 \text{ s}} = \frac{100}{60} \frac{\text{m}^3}{\text{s}} = \frac{5}{3} \frac{\text{m}^3}{\text{s}}$$
To convert volume flow rate to mass flow rate, we need the density of air ($\rho_a$). Assuming a typical density for air in air conditioning applications, let's use $\rho_a \approx 1.2 \text{ kg/m}^3$.
$$ \dot{m}_a = \rho_a \times V $$
$$ \dot{m}_a = 1.2 \frac{\text{kg}}{\text{m}^3} \times \frac{5}{3} \frac{\text{m}^3}{\text{s}} $$
$$ \dot{m}_a = \frac{1.2 \times 5}{3} \frac{\text{kg}}{\text{s}} = \frac{6}{3} \frac{\text{kg}}{\text{s}} = 2 \frac{\text{kg}}{\text{s}} $$
The Room Latent Heat is given by the formula:
$$RLH = \dot{m}_a \cdot h_{fg} \cdot (\omega_R - \omega_S)$$
where:
Now, we substitute the known values into the equation:
$$25 \text{ kW} = 2 \frac{\text{kg}}{\text{s}} \times 2500 \frac{\text{kJ}}{\text{kg}} \times (0.01 - \omega_S)$$
Since 1 kJ/kg = 1 kW/(kg/s), we have:
$$25 \text{ kW} = 2 \frac{\text{kg}}{\text{s}} \times 2500 \frac{\text{kW}}{\text{kg/s}} \times (0.01 - \omega_S)$$
$$25 = 5000 \times (0.01 - \omega_S)$$
Now, solve for $(0.01 - \omega_S)$:
$$0.01 - \omega_S = \frac{25}{5000}$$
$$0.01 - \omega_S = 0.005$$
Finally, solve for $\omega_S$:
$$\omega_S = 0.01 - 0.005$$
$$\omega_S = 0.005 \text{ kg/kg d.a.}$$
Thus, the supply air humidity ratio is 0.005 kg/kg d.a.