Land use (%) Soil group Curve number Residential, 40% C 83 Open space- good condition, 25% D 80 Commercial and business, 20% C 94 Industrial, 15% D 93
This solution details the calculation of runoff depth for a watershed based on given rainfall, land use distribution, soil types, and curve numbers (CN), using the Soil Conservation Service (SCS) method.
First, we calculate the weighted average Curve Number ($CN_{avg}$) for the watershed, considering the percentage area and CN for each land use type.
| Land Use | Area (%) | Soil Group | Curve Number (CN) | Weighted CN ($CN \times \%Area$) |
|---|---|---|---|---|
| Residential | 40% | C | 83 | $83 \times 0.40 = 33.2$ |
| Open space | 25% | D | 80 | $80 \times 0.25 = 20.0$ |
| Commercial and business | 20% | C | 94 | $94 \times 0.20 = 18.8$ |
| Industrial | 15% | D | 93 | $93 \times 0.15 = 13.95$ |
| Total Weighted CN ($CN_{avg}$) | $33.2 + 20.0 + 18.8 + 13.95 = 85.95$ | |||
The potential maximum retention ($S$) is calculated using the weighted average Curve Number ($CN_{avg}$). The formula is:
$S = \frac{25400}{CN_{avg}} - 254$
Substituting the calculated $CN_{avg}$:
$S = \frac{25400}{85.95} - 254 \approx 295.52 - 254 = 41.52 \text{ mm}$
The initial abstraction ($I_a$) is given as 0.2 times the potential maximum retention ($S$).
$I_a = 0.2 \times S$
$I_a = 0.2 \times 41.52 = 8.304 \text{ mm}$
The rainfall ($P$) is 152.4 mm. Since $P > I_a$ ($152.4 > 8.304$), runoff occurs. The SCS runoff equation is:
$Q = \frac{(P - I_a)^2}{P - I_a + S}$
Plugging in the values:
$Q = \frac{(152.4 - 8.304)^2}{(152.4 - 8.304) + 41.52}$
$Q = \frac{(144.096)^2}{144.096 + 41.52}$
$Q = \frac{20763.73}{185.616} \approx 111.866 \text{ mm}$
Rounding the runoff depth to two decimal places:
$Q \approx 111.87 \text{ mm}$
This value falls within the range specified (111.8 to 112).
| Duration (minutes) | 5 | 10 | 20 | 30 | 40 | 60 |
| Maximum depth of rainfall (mm) | 16 | 24 | 39 | 50 | 60 | 65 |
| Time from start of rainfall (min) | 0 | 20 | 40 | 60 | 80 | 100 |
|---|---|---|---|---|---|---|
| Cumulative rainfall (cm) | 0 | 0.5 | 1.2 | 2.6 | 3.3 | 3.5 |
The Curve Number (CN) of a watershed of $40$ ha area under given hydrologic soil group, land use and management practices, and Antecedent Moisture Condition (AMC)-II is $80$. The initial abstraction is $20$% of maximum retention. For the rainfall event of $40$ mm, the direct runoff in mm (round off to $2$ decimal places) is _____________