A column of size 400 × 550 mm have M25 grade of concrete and Fe415 subjected to 1700 KN of axial load. The effective length of column is 3.1 m. Determine the steel reinforcement required
1305 mm2
This problem involves determining the required steel reinforcement area for a rectangular column subjected to an axial load, based on IS 456 guidelines for concrete structures.
We are given the following information:
First, we need to calculate the factored axial load, which is the service load multiplied by a load factor of 1.5 for limit state design:
Factored Load, $P_u = \text{Service Load} \times 1.5$
$P_u = 1700 \, kN \times 1.5 = 2550 \, kN$
To use the formula for load capacity in N, we convert kN to N:
$P_u = 2550 \times 10^3 \, N$
Next, we calculate the gross area of the column cross-section, $A_g$:
$A_g = \text{Width} \times \text{Depth}$
$A_g = 400 \, mm \times 550 \, mm = 220000 \, mm^2$
According to IS 456:2000 (Clause 39.3) for a short axially loaded column, the ultimate load capacity ($P_u$) is given by the formula:
$P_u = 0.4 f_{ck} A_c + 0.67 f_y A_s$
where:
The total area of the column $A_g$ is the sum of the area of concrete $A_c$ and the area of steel $A_s$. So, $A_c = A_g - A_s$.
Substitute $A_c$ into the formula:
$P_u = 0.4 f_{ck} (A_g - A_s) + 0.67 f_y A_s$
$P_u = 0.4 f_{ck} A_g - 0.4 f_{ck} A_s + 0.67 f_y A_s$
$P_u = 0.4 f_{ck} A_g + (0.67 f_y - 0.4 f_{ck}) A_s$
We need to find the required steel area $A_s$. Rearrange the formula to solve for $A_s$:
$(0.67 f_y - 0.4 f_{ck}) A_s = P_u - 0.4 f_{ck} A_g$
$A_s = \frac{P_u - 0.4 f_{ck} A_g}{0.67 f_y - 0.4 f_{ck}}$
Now, substitute the given values into this equation:
$P_u = 2550 \times 10^3 \, N$
$f_{ck} = 25 \, N/mm^2$
$A_g = 220000 \, mm^2$
$f_y = 415 \, N/mm^2$
Calculation of $A_s$:
$A_s = \frac{2550 \times 10^3 - 0.4 \times 25 \times 220000}{0.67 \times 415 - 0.4 \times 25}$
$A_s = \frac{2550000 - 10 \times 220000}{278.05 - 10}$
$A_s = \frac{2550000 - 2200000}{268.05}$
$A_s = \frac{350000}{268.05}$
$A_s \approx 1305.76 \, mm^2$
The required area of steel reinforcement is approximately $1305.76 \, mm^2$. We compare this value with the given options.
Let's look at the options:
The calculated value $1305.76 \, mm^2$ is closest to $1305 \, mm^2$.
Therefore, the steel reinforcement required is approximately $1305 \, mm^2$. The effective length (3.1 m) is given, but for the calculation of axial load capacity using the formula $P_u = 0.4 f_{ck} A_c + 0.67 f_y A_s$, it's implicitly assumed to be a short column. A slenderness check ($L_{eff}/D$) would confirm this assumption, but the problem can be solved using the provided formula and load.
Effective length of a column is the length between the points of
Which structural member is primarily designed to resist loads perpendicular to its longitudinal axis, causing bending moments and shear forces?
For a column of length (L) and flexural rigidity (EI) which has one end fixed and other end free, the expression for critical load is given as -