A column of height h with rectangular cross-section of a × 2a has a buckling load of P. If the cross-section is changed to 0.5a × 3a and height changed to 1.5h, the buckling load of the redesigned column will be
The buckling load is a critical parameter in the design of columns, representing the maximum axial compressive load a column can withstand before it becomes unstable and deflects laterally. For long columns, this load is determined by Euler's buckling formula.
Euler's critical buckling load (\(P_e\)) for a column is given by the formula:
\[P_e = \frac{\pi^2 EI_{min}}{(L_e)^2}\]
Where:
For a rectangular cross-section with sides \(b\) and \(d\), the moments of inertia about the centroidal axes are calculated as follows:
The minimum moment of inertia (\(I_{min}\)) will always be about the axis parallel to the longer side of the rectangle, as this results in the smaller value for the formula \(\frac{base \times height^3}{12}\).
Let's consider the initial properties of the column:
To find the minimum moment of inertia (\(I_{min1}\)) for the original cross-section \(a \times 2a\):
Comparing the two values, the minimum moment of inertia for the original column is \(I_{min1} = \frac{a^4}{6}\).
Applying Euler's formula for the original column:
\[P_1 = P = \frac{\pi^2 E I_{min1}}{(K h_1)^2} = \frac{\pi^2 E \left(\frac{a^4}{6}\right)}{(K h)^2}\]
\[P = \frac{\pi^2 E a^4}{6 K^2 h^2} \quad \ldots(1)\]
Now, let's look at the properties of the redesigned column:
To find the minimum moment of inertia (\(I_{min2}\)) for the redesigned cross-section \(0.5a \times 3a\):
Comparing the two values, the minimum moment of inertia for the redesigned column is \(I_{min2} = \frac{a^4}{32}\).
Applying Euler's formula for the redesigned column:
\[P_2 = P' = \frac{\pi^2 E I_{min2}}{(K h_2)^2} = \frac{\pi^2 E \left(\frac{a^4}{32}\right)}{(K \times 1.5h)^2}\]
\[P' = \frac{\pi^2 E a^4}{32 K^2 (1.5)^2 h^2} = \frac{\pi^2 E a^4}{32 K^2 (2.25) h^2}\]
\[P' = \frac{\pi^2 E a^4}{72 K^2 h^2} \quad \ldots(2)\]
To determine the new buckling load \(P'\) in terms of the original load \(P\), we can divide equation (2) by equation (1):
\[\frac{P'}{P} = \frac{\frac{\pi^2 E a^4}{72 K^2 h^2}}{\frac{\pi^2 E a^4}{6 K^2 h^2}}\]
Notice that the terms \(\pi^2 E a^4\), \(K^2\), and \(h^2\) are common in both the numerator and denominator, so they cancel out:
\[\frac{P'}{P} = \frac{1/72}{1/6}\]
\[\frac{P'}{P} = \frac{6}{72}\]
\[\frac{P'}{P} = \frac{1}{12}\]
Therefore, the buckling load of the redesigned column will be:
\[P' = \frac{P}{12}\]
The buckling load is directly proportional to the minimum moment of inertia and inversely proportional to the square of the effective length (or height, if K is constant).
| Parameter | Original Column | Redesigned Column | Ratio (Redesigned / Original) |
|---|---|---|---|
| Height (L) | \(h\) | \(1.5h\) | \(1.5\) |
| Minimum Moment of Inertia (\(I_{min}\)) | \(\frac{a^4}{6}\) | \(\frac{a^4}{32}\) | \(\frac{a^4/32}{a^4/6} = \frac{6}{32} = \frac{3}{16}\) |
The new buckling load \(P'\) can be expressed as:
\[P' = P \times \frac{I_{min2}}{I_{min1}} \times \left(\frac{h_1}{h_2}\right)^2\]
\[P' = P \times \left(\frac{a^4/32}{a^4/6}\right) \times \left(\frac{h}{1.5h}\right)^2\]
\[P' = P \times \left(\frac{6}{32}\right) \times \left(\frac{1}{1.5}\right)^2\]
\[P' = P \times \frac{3}{16} \times \frac{1}{2.25}\]
\[P' = P \times \frac{3}{16 \times 2.25} = P \times \frac{3}{36}\]
\[P' = P \times \frac{1}{12}\]
This calculation confirms that the buckling load of the redesigned column is \(\frac{P}{12}\).