A 240 V single-phase AC supply is fed to a load resistor of 100 Ω through a thyristor. If the thyristor is fired at 90°, what is the power consumed by the load?
144 W
The question asks us to calculate the power consumed by a load resistor when a 240 V single-phase AC supply feeds it through a thyristor, fired at a specific angle. This setup describes a single-phase half-wave controlled rectifier circuit with a resistive load. A thyristor (SCR) acts like a controlled switch, allowing current to flow only after it is "fired" (triggered) at a certain point in the AC cycle, defined by the firing angle (\(\alpha\)).
Let's list the given parameters:
Our goal is to find the power consumed by the load, which can be calculated using the formula \(P = \frac{V_{rms}^2}{R}\), where \(V_{rms}\) is the RMS voltage across the load resistor.
First, we need to convert the RMS supply voltage to its peak value. For a sinusoidal AC supply, the peak voltage (\(V_{peak}\)) is related to the RMS voltage (\(V_s\)) by:
\[ V_{peak} = V_s \times \sqrt{2} \]
Substituting the given RMS supply voltage:
\[ V_{peak} = 240 \text{ V} \times \sqrt{2} \approx 240 \text{ V} \times 1.414 = 339.36 \text{ V} \]
For a single-phase half-wave controlled rectifier with a resistive load, the RMS voltage across the load (\(V_{rms}\)) is given by the formula:
\[ V_{rms}^2 = \frac{V_{peak}^2}{4\pi} \left( \pi - \alpha + \frac{\sin(2\alpha)}{2} \right) \]
Where \(\alpha\) must be in radians. Given \(\alpha = 90^\degree\), we convert it to radians:
\[ \alpha = 90^\degree = \frac{\pi}{2} \text{ radians} \]
Now, substitute \(\alpha = \frac{\pi}{2}\) into the RMS voltage formula:
\[ V_{rms}^2 = \frac{V_{peak}^2}{4\pi} \left( \pi - \frac{\pi}{2} + \frac{\sin\left(2 \times \frac{\pi}{2}\right)}{2} \right) \]
\[ V_{rms}^2 = \frac{V_{peak}^2}{4\pi} \left( \frac{\pi}{2} + \frac{\sin(\pi)}{2} \right) \]
Since \(\sin(\pi) = 0\):
\[ V_{rms}^2 = \frac{V_{peak}^2}{4\pi} \left( \frac{\pi}{2} + 0 \right) \]
\[ V_{rms}^2 = \frac{V_{peak}^2}{4\pi} \times \frac{\pi}{2} \]
\[ V_{rms}^2 = \frac{V_{peak}^2}{8} \]
Taking the square root of both sides, we get:
\[ V_{rms} = \frac{V_{peak}}{\sqrt{8}} = \frac{V_{peak}}{2\sqrt{2}} \]
We know that \(V_{peak} = V_s \sqrt{2}\). Substitute this into the expression for \(V_{rms}\):
\[ V_{rms} = \frac{V_s \sqrt{2}}{2\sqrt{2}} = \frac{V_s}{2} \]
Now, substitute the given RMS supply voltage \(V_s = 240 \text{ V}\):
\[ V_{rms} = \frac{240 \text{ V}}{2} = 120 \text{ V} \]
Finally, we can calculate the power consumed by the load resistor using the formula \(P = \frac{V_{rms}^2}{R}\):
\[ P = \frac{(120 \text{ V})^2}{100 \text{ } \Omega} \]
\[ P = \frac{14400 \text{ V}^2}{100 \text{ } \Omega} \]
\[ P = 144 \text{ W} \]
The following table summarizes the calculations:
| Parameter/Formula | Value/Calculation |
|---|---|
| Supply Voltage (\(V_s\)) | 240 V (RMS) |
| Load Resistor (\(R\)) | 100 \(\Omega\) |
| Firing Angle (\(\alpha\)) | 90\(\degree\) or \(\frac{\pi}{2}\) radians |
| Peak Supply Voltage (\(V_{peak}\)) | \(V_s \sqrt{2} = 240 \sqrt{2}\) V |
| RMS Voltage Across Load (\(V_{rms}\)) | \(\frac{V_s}{2}\) for \(\alpha = 90^\degree\) |
| Calculated Load RMS Voltage | \(\frac{240}{2} = 120\) V |
| Power Consumed (\(P\)) | \(\frac{V_{rms}^2}{R} = \frac{(120)^2}{100} = 144\) W |
Therefore, the power consumed by the load is 144 W.